Always seemed strange to me that the project didn't upgrade anything in the King's Cross area since the vast, vast majority of electric trains on the ecml pass through this area (all the TL and GN trains). Then again the feeding distance to Wood Green is scarcely more than 5 miles (132/25 supplies normally can do ~18miles) and the top speeds aren't that high.That isn't good, especially given it's on the busiest part of the ECML.
Indeed, this is the original deal with the devil for the 25kV 50Hz system as it was first developed in the 1950s. On the one hand you get fewer total substations and far less distribution equipment to deal with (as opposed to earlier forms of electrification) but on the downside you have to have neutral sections to separate OLE sections are not only on different supplies but fully 120° out of phase, and you are an ever increasing burden on the electricity supply industry. (There are quite a few other pros/cons to choosing the 25kV system I could ramble on about) I believe adjacent feeder stations typically draw from different phase combinations to try and give a vague semblance of balance.It seems that the 25kV supply is derived from a single phase which causes phase imbalances as the load is on one phase so the other two phases are at a significantly lower load.
When the earliest 25kV lines in the 1960-70s were coming about, there wasn't as much in the way of 275-400kV supergrid lines. This meant that the 132kV network (from ~the 1930s) was still being used for long distance transmission duties so the unbalanced railway load was better smoothed over. But over time the 132kV lines were relegated totally to regional distribution carrying lighter loads so the burden of railway supplies became more apparent. And in the long run generation has gone from 100% turbines to now quite mixed with power electronics, so the problem of railway connections is only more serious. I think this is finally why power electronics are making their way onto the railway with SFCs of which ECML is a pioneer in britain.I presume traditionally they had a 132kV/25kV transformer on one phase which they could get away with up to a certain power level, but increasing the power will take it beyond acceptable limits.
I've heard that SFCs or inverters more generally have been used for decades in other countries but I don't know to what extent it's been used on single-phase 25kV 50-60Hz systems? Power electronics seem to be associated with the 15kV 16.7Hz standard used in Germany, Austria, Switzerland and Scandinavia. Those systems have always needed some way to change to their nonstandard frequency from the 3-phase 50Hz grid. And because of that they still have quite a few railway power stations or large scale inverter plants. These feed a traction power network at between 55kV and 132kV all at 16.7Hz single phase spanning all the German speaking countries.From Rail Engineer: "SFCs work by taking a three-phase balanced load from a high-voltage transmission line, converting it to DC and then to a single phase 25kV OLE supply. As a result, their use does not affect the balance between the transmission line’s three phases. Hence, they can be fed from a local distribution network’s 33kV supply." https://www.railengineer.co.uk/static-frequency-converters-improving-the-25kv/