Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that? (I assume they’re neutral sections due to the fact they do it at seemingly random points)
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

Lucy1501

Member
Joined
9 Nov 2021
Messages
241
Location
Cumbria
They’re basically a piece of the overhead that aren’t connected to a power supply. It allows parts of the overhead wires to be fed from different power supplies. It also allows specific areas to be isolated for engineering works & stop faults from spreading between sections.

There are signs which mark the start and end of a neutral section, and provide prior warning. Some trains need to drop a pantograph during the section, for example, or else they’ll emergency brake.
 

skyhigh

Established Member
Joined
14 Sep 2014
Messages
6,851
Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that?
It might also just be that the driver doesn't need to accelerate any further so is just coasting.
 

GC class B1

Member
Joined
19 Jun 2021
Messages
460
Location
East midlands
They’re basically a piece of the overhead that aren’t connected to a power supply. It allows parts of the overhead wires to be fed from different power supplies. It also allows specific areas to be isolated for engineering works & stop faults from spreading between sections.

There are signs which mark the start and end of a neutral section, and provide prior warning. Some trains need to drop a pantograph during the section, for example, or else they’ll emergency brake.
I don’t think it is necessary to lower the pantograph at neutral sections. The Vacuum Circuit Breaker opens before the neutral section and closes after it to isolate pantograph from the train electrical system when passing through the neutral section.
 

hexagon789

Veteran Member
Joined
2 Sep 2016
Messages
18,295
Location
Glasgow
Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that? (I assume they’re neutral sections due to the fact they do it at seemingly random points)
Over the length of a long electrified line, it may be supplied with electricity from multiple sources, a neutral section breaks these into individually supplied sections.

I don’t think it is necessary to lower the pantograph at neutral sections. The Vacuum Circuit Breaker opens before the neutral section and closes after it to isolate pantograph from the train electrical system when passing through the neutral section.
It isn't in the UK, other countries may differ.
 

Efini92

Established Member
Joined
14 Dec 2016
Messages
2,137
They’re basically a piece of the overhead that aren’t connected to a power supply. It allows parts of the overhead wires to be fed from different power supplies. It also allows specific areas to be isolated for engineering works & stop faults from spreading between sections.

There are signs which mark the start and end of a neutral section, and provide prior warning. Some trains need to drop a pantograph during the section, for example, or else they’ll emergency brake.
What train needs to drop its pantograph through a neutral section?
 

John Webb

Established Member
Joined
5 Jun 2010
Messages
3,756
Location
St Albans
Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that? (I assume they’re neutral sections due to the fact they do it at seemingly random points)
Another reason for the driver going into 'coasting' mode is because there is another train in front of them, and the driver is adjusting the speed of their train to match the speed of the train in front by observing the signal aspects changing as they approach the signals. (There are many more signals than 'Neutral Sections' so this 'coasting' can occur almost anywhere.)
 

Snow1964

Established Member
Joined
7 Oct 2019
Messages
11,077
Location
West Wiltshire
Some will be because they are between tracks on different circuits, an example is on Royston flyover.

Each end will probably be connected to track that flyover branches from, but obviously don't want a power line linking both circuits, so put short neutral between them.

The neutral section will generally be where trains are coasting, not where they are pulling away from signals, a station, a speed restriction or motoring on steep uphill sections.
 

43066

Veteran Member
Joined
24 Nov 2019
Messages
12,089
Location
London
Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that? (I assume they’re neutral sections due to the fact they do it at seemingly random points)

You might also notice a bang if you’re sat near the pan and the driver forgets to shut off.

There are signs which mark the start and end of a neutral section, and provide prior warning.

There’s a warning board and a commencement board, no termination board provided on any that I sign.

Below is an image of a commencement board (from Wikipedia). The warning board is the same symbol in white on a black background.

IMG_2086.png
 

CAF397

Member
Joined
15 Sep 2010
Messages
1,095
Location
Lancashire
You might also notice a bang if you’re sat near the pan and the driver forgets to shut off.
The VCB bangs regardless of whether the driver shuts off or not.

The indication the driver forgot is the instant reduction in power and the sudden jolt
 

Edvid

Established Member
Joined
7 Feb 2008
Messages
2,482
There’s a warning board and a commencement board, no termination board provided on any that I sign.
There are termination and rear clear boards for overlap neutral sections (as seen on the GWML).

On a related subject, it seems inline neutrals for linespeeds above 100mph are back in vogue - two were recently installed on the MML (East Hyde / Sharnbrook) and another is apparently going in at Braybrooke.
 
Last edited:

800301

Member
Joined
29 Dec 2022
Messages
532
Location
Essex
The VCB bangs regardless of whether the driver shuts off or not.

The indication the driver forgot is the instant reduction in power and the sudden jolt

and this would happen because there is track fitted equipment small yellow blocks that talk to train fitted equipment that tells the VCB to open and close when passing through these sections. While the driver should always shut off while passing through a neutral section, as long as the APC (Automatic power control) equipment is working, it should prevent anything bad happening if the driver forgot to shut off, if it’s defective each train will be stopped at a suitable place and instructed to shut off while passing the section just to be sure
 

59CosG95

Established Member
Joined
18 Aug 2013
Messages
6,855
Location
Beeston (Notts)
There are termination and rear clear boards for overlap neutral sections (as seen on the GWML).

On a related subject, it seems inline neutrals for linespeeds above 100mph are back in vogue - two were recently installed on the MML (East Hyde / Sharnbrook) and another is apparently going in at Braybrooke.
The one at Sandridge (which East Hyde replaced) is due to be removed too.
 

Bald Rick

Veteran Member
Joined
28 Sep 2010
Messages
35,689
The one at Sandridge (which East Hyde replaced) is due to be removed too.

Whilst it’s called Sandridge neutral, it is very much in St Albans! (Right next to the tip, as it happens)


Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that? (I assume they’re neutral sections due to the fact they do it at seemingly random points)

To answer the OP, with a specific point, and trying to simplify….

AC electricity from the grid is generated and transmitted in 3 separate ‘phases’, each at 50hz; essentially the alternating of the current happens at slightly different times 50 x a second for each of the three phases. This frequency is carefully controlled by the grid and is the same across the whole country.

Where the railway electrification is supplied from the grid, it taps into one of these phases for any given section of electrical supply. (At many supply points, it taps into two phases, and uses them separately for two different sections.)

It is very important that these phases do not mix, as it can cause severe overloading of the electrical equipment.

Hence the neutral sections are there to keep the phases separate. Trains must disconnect from the power supply to prevent them bridging the neutral section and causing an overload both to the train and the power supply, hence the circuit breaker opening well in advance of the neutral, and closing well after. The neutral section itself is only a couple of metres long, usually.
 

TurboMan

Member
Joined
5 Apr 2022
Messages
422
Location
UK
There are termination and rear clear boards for overlap neutral sections (as seen on the GWML).
There were, but they've been removed as they were non-standard. They were installed for the carrier wire neutral sections which are around 250m long. The warning and commencement boards also had a 'LONG' suffix board but they've gone too.
 

Efini92

Established Member
Joined
14 Dec 2016
Messages
2,137
and this would happen because there is track fitted equipment small yellow blocks that talk to train fitted equipment that tells the VCB to open and close when passing through these sections. While the driver should always shut off while passing through a neutral section, as long as the APC (Automatic power control) equipment is working, it should prevent anything bad happening if the driver forgot to shut off, if it’s defective each train will be stopped at a suitable place and instructed to shut off while passing the section just to be sure
It’s a bit less technical than that, the yellow blocks are magnets.
 

Falcon1200

Established Member
Joined
14 Jun 2021
Messages
6,530
Location
Neilston, East Renfrewshire
and this would happen because there is track fitted equipment small yellow blocks that talk to train fitted equipment that tells the VCB to open and close

Unless the APC magnets have been stolen! (which happened in the Motherwell area a few years ago).

There are also neutral sections at locations where it has not been possible to achieve clearance between the OLE and structures; For example, on one line (the Down Inner Circle) between Queens Park (Glasgow) and Pollokshields East, due to a pipe overhead (at an angle, hence only one line affected) and at Tams Brig, Newton-on-Ayr.
 

jfollows

Established Member
Joined
26 Feb 2011
Messages
10,084
Location
Wilmslow
I also remember when the neutral section between Levenshulme and Heaton Chapel was moved (quite a few years ago) that the old APC magnets were left behind for a while, which was a bit of a pain.
 

Sly Old Fox

Member
Joined
21 Jul 2008
Messages
448
Location
England
There were, but they've been removed as they were non-standard. They were installed for the carrier wire neutral sections which are around 250m long. The warning and commencement boards also had a 'LONG' suffix board but they've gone too.

They’re still there at St Brides.
 

TurboMan

Member
Joined
5 Apr 2022
Messages
422
Location
UK
They’re still there at St Brides.
I just had a look at the route video...so they are! After all the fuss about the signage at Maidenhead being non-standard and having to be recovered...

== Doublepost prevention - post automatically merged: ==

I also remember when the neutral section between Levenshulme and Heaton Chapel was moved (quite a few years ago) that the old APC magnets were left behind for a while, which was a bit of a pain.
I suppose at least if they were all left in place, the VCB would open and then close again. Whereas if they'd left one set behind...
 