The one at Sandridge (which East Hyde replaced) is due to be removed too.
Whilst it’s called Sandridge neutral, it is very much in St Albans! (Right next to the tip, as it happens)
Something i always notice on Electric multiple units is that they sometimes just stop making a motor noise and stop accelerating, and this is always on ones where the pantograph is up. Why is that? (I assume they’re neutral sections due to the fact they do it at seemingly random points)
To answer the OP, with a specific point, and trying to simplify….
AC electricity from the grid is generated and transmitted in 3 separate ‘phases’, each at 50hz; essentially the alternating of the current happens at slightly different times 50 x a second for each of the three phases. This frequency is carefully controlled by the grid and is the same across the whole country.
Where the railway electrification is supplied from the grid, it taps into one of these phases for any given section of electrical supply. (At many supply points, it taps into two phases, and uses them separately for two different sections.)
It is very important that these phases do not mix, as it can cause severe overloading of the electrical equipment.
Hence the neutral sections are there to keep the phases separate. Trains must disconnect from the power supply to prevent them bridging the neutral section and causing an overload both to the train and the power supply, hence the circuit breaker opening well in advance of the neutral, and closing well after. The neutral section itself is only a couple of metres long, usually.