The volt-free contact that you mention is the first-filament fail alarm to warn the techs, so that they can replace the bulb (hopefully before the backup filament fails):Interesting - the circuitry we were given shows a second voltage-free contact on the lamp-proving relay going to the monitoring equipment in the supervising box. with no further current sensing. I'm unclear how you could further sense the current in a trackside Location cabinet or relay room - it would have to be done on the 100V supply at about a quarter the current - plus whatever the transformer takes on its own. Is it possible this sensing was developed after our 1970s heads were put into use?
The common bulb of the past few decades is the SL35, with two independent filaments each rated at 24 watts. There’s a small relay in series with the “main” filament: if that filament fails, the relay drops out and changes over to the “auxiliary“ filament. That then triggers an alarm to the local technicians that one of a group of signals is working on its ‘auxiliary“ filament and needs attention.
The LAMP proving (as opposed to the first-filament proving) is done in the trackside equipment case. As I explained in post #21, with a relay interlocking, this would be done with a current-sensing relay (BR Spec 941 if I remember correctly), wired in series with the 110v AC signal feed. This relay has a small transformer/rectifier built into the same case as the relay. With SSI, the signal circuit is wired back to an input on the signal module, where it is fed through a resistor, and the voltage drop across this resistor is detected.
Lamp proving was in use long before the SL35 signal heads were developed.