ECML Power Supply Upgrade
WAO
10 Mar 2019
Many thanks for the very clear schematics.
Might it be possible to mark the transformer ratings at the FS sites? These could range from 7.5 to 26.5MVA IIRC for classic and 40 MVA up to AT.
I like the diagrammatic representation of the overlap neutral sections (what used to be called quarter distance TSC's). Also, what is the distinction between MPTSC and MPTSL; is it just a change of nomenclature?
Thanks again,
WAO
thecrofter
16 Dec 2011
Historically a TSC would be a building (cabin) with the switchgear enclosed within. A location (TSL) was chosen to cater for sites with externally mounted switchgear (SMOS) - Structure Mounted Outdoor Switchgear.
WAO
10 Mar 2019
Thanks - that tells you bring an umbrella along with your Avo!
WAO
5 Aug 2015
Norfolk
Leighton Buzzard MPTSC IIRC.
Thanks! I think this should be the last piece of jigsaw in my basic chronology of AC ECRs (except for pitsea ecr, that one's lost to history
Thank you! I absolutely would if i knew them. The ukpn docs i found may inform me about the ratings in 2014 for locations between bretton and ferme park (I'll have a look later)
I would also like to add intermediate TSC locations which might be able to do if i scrub a few hours of cabride footage. Signalling power supplies would be another thing but they're even harder to find.
I'd been calling them alternative midpoints. I was surprised to find out south kirkby is normally bypassed with the whole leeds line fed from one point. I suppose the leeds line is not that busy (for electric traction).
The other benefit with these maps is that i can now easily build show alternate/degraded feeding arrangements just by changing the colours around
Yeah as said, inside switchgear vs outside switchgear. The other name ive seen is "track sectioning site" (tss) - which i don't like as much because it conflicts with "traction substation" stepping down HVAC and rectifying to DC
5 Aug 2015
Norfolk
Fantastic Diagrams! What is the signficance of the different line style for the areas fed by Corey's Mill ATFS?
2x25kV AT feeding. Normal lines are for the classic types (boosteless, RC/BT, rail return). I believe the borders of AT are welwyn and hitchin.
It also might not even yet be feeding in AT
thecrofter
16 Dec 2011
I could help you with all the ECML sites (inc. Leeds North West) but only as they were up to 2019. I visited every one during the SCADA upgrade project with the exception of Benton FS. Still bugs me to this day!
WAO
10 Mar 2019
Is it correct to describe the overlap "neutral" sections as MP as they do not separate the FS supplies when the pantograph bridges the sections?
WAO
5 Aug 2015
Norfolk
WAO
Perhaps not, it depends mostly on how I conceptualised the terminology when I first used it. To me, the humble TSC (occasionally called intermediate TSC) is a substation where either side will always be on the same supply no matter what. Whereas the MPTSC is where supplies meet. Even in the platonic ideal of: dual FS — MP — dual FS etc, the midpoint will be bypassed with the same supply on either side in N-2. So an alternative MP is just one that is bridged in Normal feeding but may not be in N-1 or -2. You will also find all sorts of oddities like Copper Mill Jnc where four lines and only two supplies meet. Trains from Hackney towards Tottenham or Chingford go through neutral sections to reach the same supply on either side. Only if you're coming up from the bottom left (Stratford) do you go from green to red supply.
I think because of this, pictures I've actually seen of displays in AC ECRs don't mention a designation of what kind of substation you're looking at (In a way that I expected they would). To them, a substation is where OLE track wires are united at a busbar through circuit breakers. On mimic displays and the like, whether or not a substation has a busbar circuit breaker+OLE neutral section, and/or one or two grid connections - is conceptually treated like a local variation to that substation. I've also found plenty of neutral sections with no substation associated with them, typically when different schemes happen to pass each other. The only way to bridge those gaps would be with the OLE switches that may or may not be manually operated.
Anyway - you don't have to agree with me on alternative mid-point, I'm just explaining my rationale. There are several times I've seen examples of something we would all agree was MPTSC just called TSC.
That would be very helpful - we could do a fill in the blanks here. It's not that important if you don't have the exact mileages, I'm putting them in for orientation around those I have for neutral sections. Where I don't have info on an OHNS past of present I've put ~ for "around about".
[see #405]
thecrofter
16 Dec 2011
Apologies for the delayed reply, but mileage wise I'm struggling to complete your list. Substations are not shown in the Sectional Appendix as you probably know and East Coast Electrification diagrams don't annotate the mileage of the sites as they're not necessarily on or near the line, so the nearest I can place a site is by the closest OLE structure number (usually by an associated switching structure) which are measured in Kilometres so here we go - hope this helps:
Holloway TSC - E2/24
Ferme Park FS - E06/24
Nene FS - E122/28
Essendine FS - E142/10
Newark FS - E195/21
Balne TSC - E267/02
Colton Junction TSC - E294/16 (there was no neutral section removed from here as it was just an insulated overlap)
Ulgham FS - E468/09
Crews Hill - EH18/26
Hare Park - EB24/29
Ardsley FS - EB27/28
Marsh Lane - EB48/17
Others:
Leeds - Skipton
Shipley TSL - LS330/23
Steeton TSL - LS345/29
Skipton TSL - LS355/41
Ilkley Branch
Greenbottom TSL - AY329/15
Ilkley TSL - AY339/23
Just for clarity, Ferme Park FS, Nene FS, Newark FS and Ulgham Crossing FS are/were Tee feeds so there is/was no Neutral Section there. Other non mid-point TSCs marked ~ also do not have a NS.
5 Aug 2015
Norfolk
Thank you for those. The mileages are not that important to me, mostly for orientation especially for places I've never heard of, and perhaps to investigate approx. how long feeding distances are and the spacings of iTSCs.
I also went back and looked up at the original maps posted on the first page of this thread (message #7) and they mention some more substations.
- digswell TSL just north of welwyn
- claypool tsc between grantham and newark
- tuxford tsc between north muskham and retford
- tollerton tsc between york and dalton
Some of these would have been listed because they were to be removed i think.
They also do list colton jnc as an mptsc, but (even stranger) they have Holme and Huntingdon both as midpoints!
thecrofter
16 Dec 2011
Yes, it's nearly right. It's Claypole (not Claypool) and Huntingdon and Colton Jn were definitely not Midpoints. Approximate locations of those others are (in rounded km):-
Digswell TSL - 34 km
Claypole TSC - 186 km
Tuxford TSC - 211 km
Tollerton TSC - 318 km
As added interest to your project, the old Biggleswade TSC was removed (after the Corey's Mill scheme went live), refurbished and reconfigured by Areva (Alstom) at Stafford to become the replacement Feeder Station at Dunton (Thameside line near Laindon in Essex) after the original brick building was literally demolished by a switchgear explosion!
Richard123
11 Nov 2018
Rugby
Colton Jn was planned to get a neutral section on the Leeds lines to allow Ravensthorpe to feed to the ECML if required. So it could have been called an MPTSC by some people. Normally Hambleton feeds through it towards Micklefield.
Originally, the Micklefield to Selby line was planned for electrification under Transpennine Electrification, before that project was cancelled, and Hambleton Jn still includes all the switchgear for that line… should it ever be reinstated!
5 Aug 2015
Norfolk
I think Colton viewed as an mptsc can be explained, but Huntingdon and Holme is just bazaar - maybe a whole mistake?
This means there was another mistake in my maps in that the original midpoint between doncaster and york was Hambleton Junction as well - but as an MPTSC. Just checked the 2001 SA I have.
That is quite interesting! Was LTS running without 2 grid supplies for a while then?
I think the arrangement is this, could be wrong though
5 Aug 2015
Norfolk
(Been a while, sorry)
Probably best to reformat the substation list, try out the table format?
The "incoming supplies" column describes the equipment at the Network Rail owned site and is about trying to indicate the fairly common occurrence where an FS has 2 grid connections but either only one is normally used (eg: Welwyn, Bytham, Grantham) or only one can be used at any one time due to lack of a neutral section (eg: Essendine, Ardsley,) - if I happen to have come across any info on transformer ratings I'll put that here too - these are gathered from OpenData sources on DNO websites although is incomplete (UKPN info are summer time ratings) ; FSC is firm supply capacity which was published for Kings Cross-Reston as part of infrastructure capability modelling done during the planning of the December 2025 timetable.
The "GSP name" refers to the site owned and operated by the 'grid company' (of various flavours) where the 25kV supply transformers are. Sometimes there is dedicated substation that just house xyz/25kV transformers which often has a name very similar to the NwR feeder station (like Durham Rail or BR Welwyn) or a name that's very different (Ryhall vs Essendine). In these cases, the "Upstream Connection" info tells you what grid infrastructure actually supplies those 25kV transformers. Elsewhere, however, the 25kV transformers are located within a larger substation that has other local connections feeding off it. At DNO sites, the 25kV transformers will be attached directly to the 132kV busbar that is also supporting 66,33,20 or 11kV transformers and/or other 132kV lines (eg: Grantham North, Kirkstall C). At transmission operator sites (NG/SPT), the railway transformers are attached to the 275kV or 400kV busbars that also are supplying 132kV (or other) transformers for DNO usage (eg: Wymondley, Portobello).
Main Route
ECML London – York (ECM 1/LN101, ECM 2–4/LN600)
(datum = Kings Cross)
MileageNameTypeNeutral SectionIncoming suppliesGSP Name/LocationUpstream ConnectionNotes
~1.14HollowayTSCNoE2/24
~3.74Ferme ParkFSNox1 18MVA; FSC 20MVA, feeds Kings Cross – Wood GreenBR Ferme Park 132/25kV (UKPN London)Tottenham-Hornsey 132kV lineE06/24
5.15Wood GreenFSYesx1 18 MVA; FSC 20MVA, feeds Bowes Park – Hertford NorthBR Wood Green 132/25kV (UKPN London)Tottenham-Hornsey 132kV line
13.21Potters BarTSCRemoved
19.29WelwynFS/SATSYesx2 supplies (18MVA), x1 on standby; FSC 21MVA,
feeds south to Wood Green
BR Welwyn 132/25kV (UKPN Eastern)
Rye House-Welwyn Grid 132kV lineSouthern extent of AT
~21.10DigswellTSCNono AT?
25.73Langley JunctionSATS/TSCYesTSC for Hertford line
29.77Coreys MillATFSYesx2 (50kV) 80MVA; FSC 40MVA,
feeds south to Welwyn + Hertford North, and north to Little Barford + Litlington
(25kV transformers at) NG Wymondley 400kVNG Wymondley 400kV
~32.50HitchinSATS/TSCMainline NS removed,Northern extent of AT
40.58BiggleswadeTSCYesNormally bridged
49.72Little BarfordFSYesx2 supplies (21MVA), x1 on standby; FSC 21MVA, feeds to Holme(25kV transformers at) NG Eaton Socon 400kVNG Eaton Socon 400kV
~59.20HuntingdonTSCNo (removed?)Some suggestion this was once an MPTSC
69.00HolmeTSCYesNormal midpoint
~76.09(former) NeneFSNox1 18MVA, see BrettonPreviously FS, E122/28
78.14BrettonFSYesx2 supplies (18MVA), x1 on standby; FSC 12MVA
feeds south to Holme
x1 BR Bretton 132/25kV (UKPN Eastern)
x1 transformer at UKPN Peterborough Cn.
x1 Stamford/Bourne 132kV line,
x1 Peterborough Cn. 132kV s/s
Peterborough Central 132/25kV supply formerly went to Nene
84.56TallingtonTSCRemovedpossibly completely gone?
~88.60EssendineFSNox2 80MVA, x1 on standby; FSC 40 MVA, feeds Bretton – Grantham NorthRyhall 400/25kV NGCottam–Wymondley 400kVE142/10
92.29BythamFSYesx2 supplies (18MVA), both on standbyBourne West 132kV (only serves railway)(NGED East Mids)Grantham South-Bourne 132kV line
100.00StokeTSCRemoved
107.55Grantham NorthFSYesx2 supplies (24MVA), both on standby(25kV transformers at) Grantham North 132kV (NGED East Mids)Staythorpe C – Bicker Fen 132kV line
~115.46ClaypoleTSCNo
121.40(former) NewarkFSNox1 supply see North Muskham
(25kV transformer at)
Staythorpe B 132kV via ~5.5km 25kV overhead powerline
NG Staythorpe 400/132kVformer FS, no longer anything
25kV powerline now extended to North Muskham
123.40North MuskhamFSYesx1 supply diverted/extended from former Newark FS as backup; FSC 14MVA, feeds south to Grantham Northpreviously TSC + NS
~131.09TuxfordTSCNo
139.41RetfordFSYesx2 supplies (18 MVA), both on standbyBR Retford 132/25kV (NGED East Mids)Staythorpe C – West Burton 132kV line
147.58BawtryTSCYesNormally bridged
~153.78Potteric CarrFSNox1 SFC supply (30.5MW), from 1x 33/25kV transformer, from 2x 33kV connections (1x as backup); FSC 27.1 MVA, feeds Doncaster – North Muskham2x 33kV from adjacent Mallard Way 132/33kV (NPG Yorkshire)West Melton 132kV
156.50DoncasterTSCYesNormal Midpoint, former dual FS
~165.70BalneTSCNoE267/02
174.56Hambleton JunctionFSYes2x SFC supplies, 2x 57MVA 132/25kV transformers, 2x 132kV connections; FSC 42 MVA, feeds south to Doncaster + South Kirkby and north to YorkHambleton Crossing 132kV (NPG Yorkshire) - built for the railwayFerrybridge – Osbaldwick 132kV line
183.75Colton JunctionTSCNoE195/21
ECML York – Newcastle (ECM 5–6; LN600)
(datum = York station)
MileageNameTypeNeutral SectionIncoming suppliesGSP Name/LocationUpstream connectionNotes
02.04YorkFSYesx2 18MVA supplies, x1 on standby; FSC 10.87MVA, feeds to Dalton(25kV transformers at) NG Poppleton 275kVNG Poppleton 275kV
~09.08TollertonTSCNo
19.09DaltonTSCYesNormal Midpoint
28.59Longlands JncTSCNo
35.05Hutton BonnevilleFSYesx2 supplies (18MVA); FSC 12MVA, feeds to Dalton and to AycliffeHutton Bonneville Rail 132/25kV (NPG Northeast)Norton – Leeming Bar 132kV line
44.47DarlingtonTSCNo
49.60AycliffeTSCYesNormal Midpoint
58.71Tursdale JncTSCNo
64.73DurhamFSYesx2 supplies (18MVA); FSC 18MVA, feeds to Aycliffe and to Chester l'stDurham Rail 132/25kV (NPG Northeast)Pennymoore – Potterhouse 132kV line
72.04Chester-le-StreetTSCYesNormal Midpoint
79.49King Edward BridgeTSCNo
ECML Newcastle – Scottish border COM (ECM 7; LN600)
(datum = Newcastle station)
MileageNameTypeNeutral SectionIncoming SuppliesGSP Name/LocationUpstream ConnectionNotes
04.23BentonFSYesx2 supplies (18MVA); FSC 12MVA, feeds to Chester l'st and to StanningtonBenton Rail 132/25kV (NPG Northeast)Tynemouth-Gosforth 132kV line
14.00StanningtonTSCYesNormal Midpoint
~20.52Ulgham CrossingFSNox2 supplies (14 MVA) in parallel & in phase; FSC 14MVA, feeds Stannington to Chathill(25kV transformers at) Linton 132kV (NPG Northeast)NG Blyth – Linton 132kV lineE468/09
33.37ShillbottleTSCYes
45.26ChathillTSCYesNormal Midpoint
57.17FenhamTSCYes
69.17Marshall MeadowsFSYesx2 supplies (10 MVA); FSC 10 MVA, feeds to Chathill and to RestonMarshall Meadows 132/25kV (SPN SPT)Low Cocklaw (aka 'Berwick') 132kV via ~4.5km single phase dual circuit 132kV overhead powerline
ECML Scottish border – Edinburgh (ECM 8–9; LN600/SC147)
(miles now count down to Edinburgh)
46.22RestonTSCYesNormal Midpoint
33.60InnerwickFSYes2x supplies (10 MVA) in parallel & in phase, feeds Reston – LongniddryInnerwick Rail 132/25kV (SPN SPT)Torness-Dunbar 132kV line
~23.23East LintonTSCNo
13.32LongniddryTSCYesNormal Midpoint
03.67PortobelloFSYes (new 2025)2x supplies (18 MVA), now both in normal use, SI feeds south to Longniddry and S2 north to Haymarket + (reverse via Millerhill) Monktonhall Jnc /(future) Sheriffhall Mains(25kV transformers at) SPT Portobello 275kVPortobello 275kV
-02.11 (EGM2 45.05)Haymarket WestTSCYesNormal Midpoint
Hertford Loop (HDB/LN120)
MileageNameTypeNeutral SectionNotes
05.78 (dn)/ 06.05 (up)(Wood Green)(FS)Yes (named "Bowes Park")see ECML Ldn-York
~11.40Crews HillTSCNoEH18/26
19.76Hertford NorthTSCYesNormal Midpoint
27.47 (dn)/ 27.69 (up)(Langley Jnc)(TSC)Yessee ECML Ldn-York
Leeds Line
Doncaster – Leeds (DOL 1–2/LN836)
156.50(Doncaster)(TSC)Yessee ECML Ldn-York
165.35South KirkbyTSCYesNormal midpoint
~171.70Hare ParkTSCNoEB24/29
~180.17ArdsleyFSNo1x 18MVA
1x 10MVA
(one of these is standby)
Ardsley FSC = 6MVA
feeds South Kirkby – Copley Hill
1x 18MVA from
Scampston Drive 132/25
1x 10MVA from
Station Lane 132/25
(adjacent to each other) (both NPG Yorkshire)
Skelton Grange – Rodley (and Staygate) 132kV line
185.57Leeds "Copley Hill"TSLYes1x feeder cable from ArmleyNormal Midpoint
TPML: Leeds - York
Leeds – Micklefield Jnc (HUL4; LN836, LN898)
(miles count down from Leeds station (HUL4 20.50) towards datum at Selby Jnc)
MileageNameTypeNeutral SectionIncoming SuppliesNotes
~20.00(former)Marsh LaneTSLNoEB48/17 Replaced by Neville Hill
~18.??[Neville Hill]TSCNo1x feeder cable from Armley
(previously went to Marsh Lane)
under construction?
~10.63[Micklefield]TSCYes(planned midpoint)
Micklefield Jnc - Church Fenton (CFM; LN 902)
(miles count down from Micklefield Jnc (CFM 15.62) towards datum at York)
- n/a
Church Fenton (North Jnc) - Colton Jnc (NOC; LN 854)
(miles count down from Church Fenton North Jnc (NOC 10.37) towards datum at York)
~10.??Church FentonTSCNoVery unconfirmed, could even be on CFM or the other (south) side of the station.
(5.41)(Colton Jnc)(TSC)On NOC Yes?TSC with ECML, likely has carrier-wire type neutral section on transpennine line
Airedale/Wharfdale
Leeds (Whitehall) – Skipton (TJC3 (part); LN922)
(Whitehall West Jnc at 195.57, counting higher as you go northwest, datum = St Pancras)
196.13ArmleyTSLYesNormally bridged, Cables to Copley Hill and to Neville Hill (previously Marsh Ln)
197.21KirkstallFSYes2x 18.75MVA; FSC 14MVA, feeds east to Copley Hill + (future) Micklefield and west to Bingley + Ilkley + Bradford(25kV transformers at) Kirkstall C 132kV (NPG Yorkshire)Kirkstall B 275/132KV
202.15ApperleyTSLYesNormally bridged
~205.04ShipleyTSLNoLS330/23
209.21BingleyFSYes1x 18.75MVA; FSC 14 MVA, feeds west to Skipton(25kV transformer at) Bingley 132kV (NPG Yorkshire)Bradford West – Bingley 132kV line
~214.30SteetonTSLNoLS345/29
~220.47SkiptonTSLNoLS355/41
Shipley – Bradford (SBF/LN922) and Shipley South – West (BIB/LN932)
(same datum as TJC)
- n/a
Ilkley branch (ILK1–2/LN924)
(same datum as TJC)
202.15(Apperley)(TSL)YesSee Leeds-Skipton
~204.32GreenbottomTSLNoAY329/15
~210.51IlkleyTSLNoAY339/23
Baildon branch (GUE 2/LN926)
(same datum as TJC)
- n/a
  • DNO = Distribution Network Operator (a generic term)
    • In England/Wales: owner, maintainer and operator of infrastructure between 230V and 132kV
    • In Scotland: owner, maintainer and operator of infrastructure between 230V and 66kV
  • License Area = Geographic subdivision of the distribution network (13 areas numbered from 10–23)
  • Transmission network:
    • In England/Wales: 275kV and 400kV infrastructure
    • In Scotland: 132kV, 275kV and 400kV infrastructure
  • NG = National Grid: an electricity company that owns
    • National Grid Electricity Transmission (NGET)
      • owns/maintains transmission network in England/Wales
    • National Grid Electricity Distribution (NGED): the DNO for
      • East Midlands (license area 11)
      • West Midlands (license area 14)
      • South Wales (license area 21)
      • South West England (license area 22)
  • SPEN = ScottishPower Energy Networks: an electricity company that owns
    • SP Transmission (SPT)
      • owns and maintains transmission network in Southern Scotland
    • SP Distribution
      • DNO for Southern Scotland (license area 18)
    • SP Manweb
      • DNO for Merseyside and North Wales (electricity board) (license area 13)
  • SSEN = Scottish & Southern Electricity Networks: an electricity company that owns
    • Scottish Hydro-Electric Transmission (SHE Transmission)
      • owns and maintains transmission network in Northern Scotland
    • Scottish Hydro-Electric Power Distribution
      • DNO for Northern Scotland (license area 17)
    • Southern Electric Power Distribution
      • DNO for "Southern England" (license area 20) covering Hampshire/Wiltshire/West London/Oxfordshire
    • (any of the above may be called "SSEN" or "S & S")
  • UKPN = UK Power Networks: an electricity company that owns
    • Eastern Power Network
      • DNO for Eastern England (license area 10)
    • London Power Network
      • DNO for London (license area 12)
    • Southern Power Network
      • DNO for South East England (license area 19) around Kent/Sussex
  • NPG = Northern Powergrid
    • NPG Yorkshire
      • DNO for Yorkshire (license area 23) around South/West Yorkshire
    • NPG North(east)
      • DNO for North East England (license area 15) covering North Yorkshire and The Northeast
  • Electricity Northwest
    • DNO for North West England (license area 16) covering Lancashire and Cumbria
  • NESO = National Electricity System Operator
    • Actually operates all the transmission infrastructure, recently nationalised (used to be another subsidiary of NG)
    • NGT, SHE-T and SPT don't actually operate minute-to-minute the networks they own, whereas the DNOs do.
Terms relating to voltage hierarchy
  • Transmission, aka "Supergrid"
    • 400kV, 275kV
    • (under construction: 525kV HVDC)
  • Sub-transmission, aka "Grid".
    • 132kV
  • Primary distribution, aka "Extra-High Voltage (EHV)"
    • 66kV, 33kV, 22kV
    • (33kV is the most common)
  • Secondary distribution, aka "High Voltage (HV)"
    • 20kV, 11kV, 6.6kV
    • (11kV is the most common)
  • Low Voltage (LV)
    • 400V 3 phase, 230V single phase
@GraphitProjekt - I’m not quite sure if it’s the best choice to use ‘via Berwick’ in the context of Marshall Meadows. It’s certainly fed from the ‘Berwick area’ DNO substation, but the physical location is some way west of Berwick, at a site called Low Cocklaw.
5 Aug 2015
Norfolk
I think my idea was that it all comes from Eccles 400/132 but the single phase 132kV powerline comes from Berwick Grid. I admit, I've been somewhat inconsistent about where i draw the line in the GSP collumn
thecrofter
16 Dec 2011
MileageNameTypeNeutral SectionIncoming SuppliesGrid ConnectionNotes
04.23BentonFSYesx2 18MVATynemouth-Gosforth 132kV line
~20.52Ulgham CrossingFSNox2 supplies, x1 on standbyLinton 132kV s/sE468/09
57.17FenhamTSCYes
69.17Marshall MeadowsFSYesx2 suppliesEccles 400/132kV via Berwick
Minor amendment to your list above for normal feeding.
Ulgham FS has two feeds from the same source (and phase) feeding one busbar with both incoming circuit breakers normally closed. F1 feeds South and F2 feeds North by switching around an Insulated Overlap such that F1 feeds south to Stannington Neutral Section and F1 feeds north to Chathill NS through (and around Shilbottle NS) via a Normally Closed bus section there.
Worth noting that Ulgham also has two Harmonic Filters associated with the incoming feeds to dampen the high level of harmonics produced by the aluminium smelting works fed by Linton.
The Alcan smelting works were demolished about 10 years ago, so have the filters survived the upgrades to Ulgham? I found a planning application that shows the original buildings and the two 1990s harmonic filter cabins all due to be removed.
thecrofter
16 Dec 2011
Ah - it's obviously been a while since I was last there!
That's really interesting, this must be a pretty rare arrangement. Is this also the case with Ardsley?
It is unusual yes. Ardsley has two incoming feeds but only one in use. The other is in effect a standby supply.
5 Aug 2015
Norfolk
Thanks for that, table and illustrations have been updated.
I also found out that Bingley only has one transformer so it must be only feeding to Shipley. This means that everything from Leeds to Bingley including Bradford and Ilkley comes off Kirkstall FS. The whole arrangement around Leeds seems quite flexible with Armley and Apperley midpoints normally bridged and extra cables from Armley to Copley Hill and to Marsh Lane or Neville Hill.
(There was a TRUP announcement a year or so ago about a new cable from Armley to a new Neville Hill substation, but I have seen previous indication a cable always went to Marsh Lane).
I wonder what the situations are for Armley or Apperley to actually bridge different supplies?
thecrofter
16 Dec 2011
Marsh Lane TSL was installed as part of the enabling works for the Leeds 1st Project (1999/2000) to keep Neville Hill depot alive whislt the OLE in Leeds Station was isolated during reconstruction. There is a feeder cable from Armley TSL via Whitehall Jn. running alongside the Leeds/Liverpool canal viaduct, through the back of the station and over Marsh Lane Vidauct to the TSL. Marsh Lane Circuit Breakers are interlocked with Armley to prevent paralleling of supplies. How the proposed Neville Hill site will be configured I'm afraid I don't know.
The Leeds North West feeding arrangement was like this back then:
5 Aug 2015
Norfolk
Now that I know Bingley has transformer, that's now how I have it. The other source I have is an image from a PWI presentation on Hambleton Junction SFC. This somewhat suggests Marsh Lane is no longer.
5 Aug 2015
Norfolk
Why are they labelled 'Existing' and 'Current'?
yeah it's a bit strange, but it's just before and after Hambleton Junction. (But clearly both within PSU2 because of Potteric Carr) - maybe it's 'existing installation' vs 'current proposal'
Elecman
31 Dec 2013
Lancashire
Something wing with louring of Doncaster on the Existing drawing as there is no purple area shown
stuving
26 Jan 2017
The status of Berwick substation is a bit odd. It's listed in the ETYS data under SPT (Scottish Power Transmission), so it's a transmission substation. Its feed from Eccles was recently renovated by SPT, though not upgraded. Functionally, it's a 132/33kV grid supply point, with a pair of 60 MVA transformers, though in this part of the world the DNO is SPD, also part of SPEN.
All quite logical, and like some other GSPs is was left off the transmission network schematics in ETYS. But from ETYS 2020, it has been shown - like this:
That's fine, up to a point - black is for 132 kV circuits and substations - but Marshall Meadows is not listed as as a grid substation. Nor should it be, as traction supplies are not considered part of the transmission network. And you do kind of expect the circuits shown here to be three phase. As to quite why it suddenly appears in 2020 ...
5 Aug 2015
Norfolk
Is it some kind of midway situation where potteric carr was operating but not hambleton jnc so doncaster is halfway in use. So one of the supplies is without a job because of potteric carr.
Unless you mean that Doncaster to South Kirkby was also from Doncaster?
I suppose because it's part of the scottish system, they consider 132kV to be "transmission" although it's technically in england.
There is planning permission allotted to swap the Berwick to Marshall Meadows (Low cocklaw?) circuits to be 3 phase for 2 SFCs to be installed at Marshall Meadows. But i guess they removed it from maps because suddenly that didn't happen