RichardAsh1981
Member
- Joined
- 28 Oct 2017
- Messages
- 251
I've never seen that, the labels are just T1, T2 etc. Probably helped by distribution sites being historically more separated into layers - once you know you are at a Primary site, the only sort of transformer is primary from 33kV to 11kV. An 11kV to 400V substation at the same place is often suffixed "Local" and is considered a separate site, not least because the authorisation for access is often different.hence lots of 132/33kV substations are referred to as "grid". Does this mean that a 33/xyz connection would be a PT (for primary [distribution] transformer)?
Primary sites are also often the oldest - so the naming of "XYZ Grid" substations was a way to avoid confusion when the new Grid substation was added on in the 1930s, the same as when the Super Grid was overlaid in the 1970s.
The other naming used is GSP (Grid Supply Point) for 132kV to 33kV, the historic Grid to Regional Board handover, and BSP (Bulk Supply Point) for 275/400kV to 132kV sites on the super grid.