Should the OHLE be arcing in light drizzle?

Status
Not open for further replies.

PaxVobiscum

Established Member
Joined
4 Feb 2012
Messages
2,411
Location
Glasgow
..or even at all?

Waiting for a train last night at a certain Glasgow Station, passengers were entertained by a small but noticeable son et lumière from a vertical insulator at the end of the platform. Intermittent fizzing and yellow/orange flashes (is pigeon poo rich in sodium?) Is it worth reporting, or does this sort of thing happen all the time?
I tried to take a picture on my phone but was somehow reluctant to get near enough to get a good shot. :D
 
Last edited:
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

AM9

Veteran Member
Joined
13 May 2014
Messages
16,034
Location
St Albans
..or even at all?

Waiting for a train last night at a certain Glasgow Station, passengers were entertained by a small but noticeable son et lumière from a vertical insulator at the end of the platform. Intermittent fizzing and yellow/orange flashes (is pigeon poo rich in sodium?) Is it worth reporting, or does this sort of thing happen all the time?
I tried to take a picture on my phone but was somehow reluctant to get near enough to get a good shot. :D

Its not uncommon for insulators on all high voltage lines to buzz, fizzle and sometimes have small flashovers. If it gets large enough to see sparks of glowing metal come to ground then there may be a problem. Are they as big as when a pantograph flashes in frost?
 

carriageline

Established Member
Joined
11 Jan 2012
Messages
1,897
I have never seen OHL have a flashover, and there's plenty of it out my window! It does fizz and buzz in the rain which is eerie!

If i saw it at work, I would report it.


Sent from my iPhone using Tapatalk
 

Bald Rick

Veteran Member
Joined
28 Sep 2010
Messages
35,817
If it is arcing across the insulator, it is unusual and a likely future insulator failure. So report it. It may well have been bird related.

Just buzzing is not an issue.

If it is arcing between contact wire and the pantograph when a train passes underneath the insulator, this is nothing to worry about.
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
28,665
Location
Nottingham
If you report it, it would be worth quoting the letters/numbers on the plate on the nearest pole if you know them. That will give them a definite confirmation of where any problem might be.
 

carriageline

Established Member
Joined
11 Jan 2012
Messages
1,897
Or, the better thing, would be to inform a member of station staff who SHOULD be 'in the know' of who to contact.


Sent from my iPhone using Tapatalk
 

Muzer

Established Member
Joined
3 Feb 2012
Messages
2,784
I've seen a dull blue glow during night-time drizzle on the south end of the ECML, but nothing more than that.
 

mattyoung905

New Member
Joined
17 Dec 2014
Messages
2
Yesterday I saw an arcing over of an insulator to a support at a local station: Orange sparks flashing over a few times a minute - got a little bit of flame at one point too. Mentioned it to a member of platform staff who agreed it didn't look too bad but was out of ordinary so he'd get it reported.
 

PaxVobiscum

Established Member
Joined
4 Feb 2012
Messages
2,411
Location
Glasgow
While waiting at Bellgrove today I was aware of a number of birds flying about the entrance to the tunnel under the old abbatoir, and had just stopped looking in that direction when there was a very loud explosion, a sudden cloud of smoke and feathers and no more pigeons. Nothing tripped and the trains carried on.

Not so much RIP as I squared R :)
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
28,665
Location
Nottingham
Resistance is futile!

The power may have been tripped by the pigeon demisal event, but standard practice is to try once to re-close the breaker if there is no other indication of a problem. So the power may have been off but only for a few seconds.
 

DaveHarries

Established Member
Joined
12 Dec 2011
Messages
2,574
Location
England
Can we put an end to these "shocking" puns please? If not then I will pylon the pressure. :lol:

Dave
 

PaxVobiscum

Established Member
Joined
4 Feb 2012
Messages
2,411
Location
Glasgow
We have a mast a fine collection now - a step up from the usual. We could conduct ourselves with dignity and stop now without losing phase.
We really auto tranform this in to a serious discussion again before the thread gets isolated.
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
28,665
Location
Nottingham
Did someone dropper clanger? It didn't register with me, but I suppose we will all copper penalty from the moderators if the current situation continues. We should agan try to be reasonable.
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
3,577
Location
Lancashire
I'm sure an Uncommanded OLE trip requires a wait of 2 mins by the ECR Controller before trying to reclose the breaker to give time for any phone calls re persons in contact with the OLE
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
28,665
Location
Nottingham
I'm sure an Uncommanded OLE trip requires a wait of 2 mins by the ECR Controller before trying to reclose the breaker to give time for any phone calls re persons in contact with the OLE

This report, which admittedly is from HS1, says that the breakers will automatically attempt to re-close after a few seconds. I'm not sure if they all do this, but it would explain why the controller shouldn't re-close them manually without seeking further information, as one re-closure attempt has already failed.

http://www.raib.gov.uk/publications/investigation_reports/reports_2010/report122010.cfm
 

carriageline

Established Member
Joined
11 Jan 2012
Messages
1,897
On 3rd rail at least, they will try to close it nearly straight away. If that fails they will wait a minute or 2. The idea being to get it reenergised within a few minutes, thus stops distracting phone calls from signallers! They can try up to 3 times (2 times on a single end fed section)
 

Ian1000

New Member
Joined
13 Feb 2015
Messages
3
Some small sparks / orange glows on insulators is not something to be worried about. Insulators are designed in the knowledge that pollution will be deposited on their surface. By the coast this could be salty, clearly there could be diesel particulate and other sources such as bird droppings! When this pollution gets wet - light rain / fog are particularly bad, it becomes conductive. Something called dry band arcing then occurs, the conductive layer heating up with liquid evaporating. When the liquid evaporates, you get localised arcs such as those described. Generally nothing to worry about and if the insulators are ceramic they will do no long term damage.
 

cjmillsnun

Established Member
Joined
13 Feb 2011
Messages
3,275
Some small sparks / orange glows on insulators is not something to be worried about. Insulators are designed in the knowledge that pollution will be deposited on their surface. By the coast this could be salty, clearly there could be diesel particulate and other sources such as bird droppings! When this pollution gets wet - light rain / fog are particularly bad, it becomes conductive. Something called dry band arcing then occurs, the conductive layer heating up with liquid evaporating. When the liquid evaporates, you get localised arcs such as those described. Generally nothing to worry about and if the insulators are ceramic they will do no long term damage.

Hmmmm

Dry band arcing is a result of pollution, but on composite insulators, it is definitely not a good thing, as it can degrade the insulator which could eventually cause flashover.
 

Ian1000

New Member
Joined
13 Feb 2015
Messages
3
Exactly why I said no issue for ceramics. Dry band arcing is unavoidable for composites as well, there is nothing you can do to avoid it completely. Yes, it will cause damage over a long period and the benefits of the extra hydrophobicity that the composites have / the lower weight has to be set against probable increased ageing.
 