So with this how would it be possible for the first feeder station to feed beyond the midpoint track section to its right?
Mid point substations have a circuit breaker on the busbar that is normally open, but can be closed if safe to do so. It's probably interlocked with other breakers to make sure different grid feeds never touch.
I've got down a bit of a rabbit hole
I've been burrowing since last october, there's so much fun stuff!
over the last few days of looking at railways in Europe. I didn't realise how many different voltages are used: 1.5kV DC in France and the Netherlands, 3kV DC in Belgium and 15kV 16 2/3 Hz in Germany and Switzerland.
1.5kV on mainline mixed traffic railways is a historical oddity that is now somewhat of a limitation for those countries, especially Netherlands. Japan also has loads of 1.5kV dc. With that being said, it's a modern standard for dedicated metro/suburban systems. There's a suburban line in montreal that recently went from 25kV AC to 1.5kV dc!!
3kV DC is also in Italy, Morroco, South Africa and many places that the USSR had influence.
It makes you wonder why all these different voltages were chosen, presumably due to technical limitations many decades ago.
Back in 1900 there were basically 2 options available to you. LV DC or low frequency AC.
With dc electrification you can generate 3phase ac at (historically) between 6-66kV. This often developed into whole distribution grids fully controlled by the railway and distributed to AC/DC substations for a line voltage of 600 up to 3000. This is fed straight to resistor banks to control dc motors.
Substations spacing is obviously dependent on that line voltage but i think 3000 is the limit possibly due to
- the size of motor (higher voltage=thicker insulation? Probably other reasons why optimal motor voltage is around 1kV),
- expense and practicality of dc circuit breaker and rectifier technology (in the early days susbtations were manned with dc rotary converters),
- and because the longer the length between susbtations the higher the risk that only one of the circuit breakers would actually detect a fault. (In contrast to AC, DC electrification sections are double end fed)
- Third rail requires lower voltage i assume because of the air gap to the ground. 750V for top contact, but side/bottom contact can get up to 1200V
Substation spacing for 3000V is about 7km i think. For 750V down to around 3 or 4. But of course it depends wildly on the traffic requirements and line speeds etc.
25kV AC at 50Hz is actually quite similar to old school DC. But instead of the train picking up LV DC, it connects to that HV AC distribution network (which in this case is single phase 25kV) and each train is a mobile substation stepping down and rectifying to around 1kV dc for dc motors or (later) a motor drive powering 3phase ac motors. Having a rectifier on a train was only really an option in the 1950s
For this reason, LV DC electrification is still preferred over 25kV AC where you railway is sufficiently short distance and high frequency that if the transformers and rectifiers are in standalone substations rather than on every train - you'll need to buy fewer transformer/rectifiers. A short distance/high frequency railway is otherwise known as a metro.
The low frequency AC thing is to do with 1900s era universal motors being able to work off 16.67 or 25Hz AC rather than 50Hz. Others cleverer than I can understand exactly why this is.
Obviously with AC OLE you can feed the train with a much higher voltage (historically 6.6kV and 11kV) than the motors want because you can step down on board the train, this way minimising substation count. So you can see why some 1900s railways chose this over DC if long distance was important for them.
Both systems often required railways to build power stations and HV distribution grids. (Germany, Austria and Switzerland share a single phase 16.7hz grid just for railways at transmission voltages between 55kV and 132kV). But as public electricity utilities started to appear later on in the 20th century, dc systems could more easily intergrate as they were using 3phase AC sometimes already at 50hz (though 25hz was common with these systems too). For low frequency AC though, this was more of a problem so no one would ever build this system nowadays.
There were a few early railways in the UK that used 25hz 6.6kV. Lancaster-Morecambe-Heysham and (more amusingly) South London under LBSCR: firstly london bridge to victoria but later to crystal palace and some other places. This was ripped up and replaced with 750V 3rd rail in the 1920s under SR to unify the network with the pre-existing 3rd rail out of Waterloo. I'm quite intrigued on the alternate history where southern region is all low frequency AC!
Speaking of which, HS1 and the Channel Tunnel must have a very good power capacity as each Class 374 set can draw up to 16MW of traction power. A couple of those accelerating and the power supply would know about it!
Hs1 is all 2x25kV AT. It also has regular Autotransformer susbtations every 10 or so km to make best use of it.