How come the North and West London Line's are OHLE from South Acton and Shepherd's Bush onwards despite the NLL being third rail throughout prior to becoming part of the Overground?
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

RJ

Established Member
Joined
25 Jun 2005
Messages
8,819
Location
Back office
How come the North and West London Line's are OHLE from South Acton and Shepherd's Bush onwards despite the NLL being third rail throughout prior to becoming part of the Overground?

It's also an important freight route which has had OHLE for years. Not all electric locomotives have third rail capabilities.

The NLL has dual voltage EMUs as parts of it don't have a third rail.
 
Last edited:

swt_passenger

Veteran Member
Joined
7 Apr 2010
Messages
34,257
Even before the Overground took off the Silverlink Metro 313s switched to OHLE where it was already available, IIRC because the DC system was on its last legs and current draw was restricted. Then when the TfL sponsored NLL four tracking extension was being planned, and the diversion into Stratford High Level was going to use OHLE anyway, and I think at one stage there was also a presumption that Eurostar would continue to use North Pole depot, so with all things taken together it made sense to standardise on OHLE on the majority of the NLL.
 

randyrippley

Established Member
Joined
21 Feb 2016
Messages
5,382
Essentially much of the NLL was converted to OHLE to allow electrified container trains to run from the WCML via Willesden to the East Anglian ports without needing to change locomotives. Previously the NLL transit needed a diesel
 

LNW-GW Joint

Veteran Member
Joined
22 Feb 2011
Messages
21,904
Location
Mold, Clwyd
The remaining oddity is why 3rd rail continues into Euston despite all tracks being wired.
It must make life very complicated on that final mile with mixed electrical systems.
 

etr221

Established Member
Joined
10 Mar 2018
Messages
1,584
My thoughts are (1) into Euston is dual system, and (since the WCML ac electrification in the 1960s) everything is set up for that - unless/until major changes (to what?) come along that will easier if single system, is there much/any benefit in changing? and (2) there is still objection (or at least relectance) to trains changing system on the move - which makes extending the overhead to (at least) South Hampstead desirable, if not necessary. Are clearances in the New (dc) Line Tunnels such to make this easy, or is it in the difficult category? If the later, is there a suitable space/length for on the move changing at the top of Camden bank? How do these difficulties, of facilitating trains changing system, compare to the benefit of making Euston single system? I would guess they exceed it - at least until there is change in propect to alter the balance....
 

Irascible

Established Member
Joined
21 Apr 2020
Messages
2,233
Location
Dyfneint
Even before the Overground took off the Silverlink Metro 313s switched to OHLE where it was already available, IIRC because the DC system was on its last legs and current draw was restricted. Then when the TfL sponsored NLL four tracking extension was being planned, and the diversion into Stratford High Level was going to use OHLE anyway, and I think at one stage there was also a presumption that Eurostar would continue to use North Pole depot, so with all things taken together it made sense to standardise on OHLE on the majority of the NLL.
IIRC ( it's been a long time since I took the NLL regularily & that was before Silverlink! ) the OHLE was turned off on the weekends, just for some extra complication. Fairly sure none of the platforms the freight line west of Dalston ran through were open back then, but it's been a long time.

Living in Dalston got me stuck on a fair number of trains failing to switch input system. Oddly don't remember any at Drayton Park...
 

stuu

Established Member
Joined
2 Sep 2011
Messages
3,763
The remaining oddity is why 3rd rail continues into Euston despite all tracks being wired.
It must make life very complicated on that final mile with mixed electrical systems.
Presumably because of the preference for doing it whilst stopped, which would mean stopping on the slows next to carriage sidings which would affect timekeeping
 

MarkyT

Established Member
Joined
20 May 2012
Messages
7,557
Location
Torbay
ISTR there were some lengthy stretches of dual electrification when the OHLE was first installed for freight on the NLL. This is undesirable beyond necessary short sections for changeover as there's a conflict in the earthing standards between the two systems. In DC only areas, the rails are not earthed, to encourage the large return current to stay in the rails en route back to the substation instead of taking all kinds of alternative paths through the ground and any metallic objects in the vicinity, which are at risk of damage by a form of corrosion caused by the current. By contrast, in AC areas, the traction return rail is earthed and bonded to every metallic object nearby, including electrification stanchions, signal gantries and bridges for safety with the high voltage used and to avoid the risk of dangerously high 'touch potential' that staff and passengers might otherwise be exposed to.

In a dual electrified area, the safety concerns must take precedence, so comprehensive bonding is provided, giving massive opportunity for the DC current to stray and cause damage to structural metalwork and underground utilities. The AC return current is much less of a problem if it strays as there isn't the same corrosion problem with AC and the current is so much smaller due to the high supply voltage. Stray current immediately became a problem on the NLL which concentrated minds on removing as much of the 3rd rail as possible except for unavoidable short changeover sections. For the DC lines running into Euston from Camden I believe some mitigations have been applied such as parallel reinforcing conductors, and while the fairly limited service and small trains involved don't produce the high levels of DC return current in rails south of the river, there must still be some effect and long term it makes sense to decommission the 3rd rail and have the Watford trains switch to overhead for the final run into the terminus.
 

Peter Mugridge

Veteran Member
Joined
8 Apr 2010
Messages
17,810
Location
Epsom
In a dual electrified area, the safety concerns must take precedence, so comprehensive bonding is provided, giving massive opportunity for the DC current to stray and cause damage to structural metalwork and underground utilities. The AC return current is much less of a problem if it strays as there isn't the same corrosion problem with AC and the current is so much smaller due to the high supply voltage. Stray current immediately became a problem on the NLL which concentrated minds on removing as much of the 3rd rail as possible except for unavoidable short changeover sections. For the DC lines running into Euston from Camden I believe some mitigations have been applied such as parallel reinforcing conductors, and while the fairly limited service and small trains involved don't produce the high levels of DC return current in rails south of the river, there must still be some effect and long term it makes sense to decommission the 3rd rail and have the Watford trains switch to overhead for the final run into the terminus.
What is the normal level of current ( i.e. amps ) in both these systems?
 

Steve Harris

Member
Joined
11 Dec 2016
Messages
1,193
Location
ECML
ISTR there were some lengthy stretches of dual electrification when the OHLE was first installed for freight on the NLL. This is undesirable beyond necessary short sections for changeover as there's a conflict in the earthing standards between the two systems. In DC only areas, the rails are not earthed, to encourage the large return current to stay in the rails en route back to the substation instead of taking all kinds of alternative paths through the ground and any metallic objects in the vicinity, which are at risk of damage by a form of corrosion caused by the current. By contrast, in AC areas, the traction return rail is earthed and bonded to every metallic object nearby, including electrification stanchions, signal gantries and bridges for safety with the high voltage used and to avoid the risk of dangerously high 'touch potential' that staff and passengers might otherwise be exposed to.

In a dual electrified area, the safety concerns must take precedence, so comprehensive bonding is provided, giving massive opportunity for the DC current to stray and cause damage to structural metalwork and underground utilities. The AC return current is much less of a problem if it strays as there isn't the same corrosion problem with AC and the current is so much smaller due to the high supply voltage. Stray current immediately became a problem on the NLL which concentrated minds on removing as much of the 3rd rail as possible except for unavoidable short changeover sections. For the DC lines running into Euston from Camden I believe some mitigations have been applied such as parallel reinforcing conductors, and while the fairly limited service and small trains involved don't produce the high levels of DC return current in rails south of the river, there must still be some effect and long term it makes sense to decommission the 3rd rail and have the Watford trains switch to overhead for the final run into the terminus.
Exactly this ^

As the whole NLL was originally+ third rail from Richmond to North Woolwich, then (as stated up thread) parts gained OHLE to let freight get between the WCML (Primrose Hill) and the GEML (Stratford High Level). When Class 313's* got transferred to run the NLL services some parts of the 3rd rail system was ripped out because of the above !

*313's being dual voltage units, were as previously pure 3rd rail units had been used.

+ OK, probably not since time internal, but certainly when I travelled the line in the early 1980's.
 

MarkyT

Established Member
Joined
20 May 2012
Messages
7,557
Location
Torbay
What is the normal level of current ( i.e. amps ) in both these systems?
I can't find any info online about the installed power of the class 710 units but let's assume they're rated at about 2000kW. To deliver that power at 750VDC a current of 2666A is required. The same power on 25kVAC would draw around 80A.
 

Bikeman78

Established Member
Joined
26 Apr 2018
Messages
6,172
I can't find any info online about the installed power of the class 710 units but let's assume they're rated at about 2000kW. To deliver that power at 750VDC a current of 2666A is required. The same power on 25kVAC would draw around 80A.
If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.
 

Peter Mugridge

Veteran Member
Joined
8 Apr 2010
Messages
17,810
Location
Epsom
I can't find any info online about the installed power of the class 710 units but let's assume they're rated at about 2000kW. To deliver that power at 750VDC a current of 2666A is required. The same power on 25kVAC would draw around 80A.

If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.
Thank you both. :)
 

Richard Scott

Established Member
Associate Staff
International Transport
Railtours & Preservation
Joined
13 Dec 2018
Messages
4,576
If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.
I think maximum draw is around 4000amps or just over for 3rd rail and around 200amps for 25kV overheads? Means 12 car CIGs etc would be limited when accelerating? Know if too many trains left a London Terminus at once the power sometimes tripped due to excessive current draw so 3rd rail quite limited. Know a 2 car EPB wasn't ever going to cause these sorts of problems on NLL!
 

Ken H

Established Member
Joined
11 Nov 2018
Messages
6,718
Location
N Yorks
When cl 313 replaced cl 501, drivers found that on dual electrifies parts, the 313's accelerated better in AC mode. So using AC allowed them to keep time better. Quite within the rules.

More 25kv was added and I think only the furthest west section is 3rd rail.

Found this old thread
 