How come the North and West London Line's are OHLE from South Acton and Shepherd's Bush onwards despite the NLL being third rail throughout prior to becoming part of the Overground?
How come the North and West London Line's are OHLE from South Acton and Shepherd's Bush onwards despite the NLL being third rail throughout prior to becoming part of the Overground?
IIRC ( it's been a long time since I took the NLL regularily & that was before Silverlink! ) the OHLE was turned off on the weekends, just for some extra complication. Fairly sure none of the platforms the freight line west of Dalston ran through were open back then, but it's been a long time.Even before the Overground took off the Silverlink Metro 313s switched to OHLE where it was already available, IIRC because the DC system was on its last legs and current draw was restricted. Then when the TfL sponsored NLL four tracking extension was being planned, and the diversion into Stratford High Level was going to use OHLE anyway, and I think at one stage there was also a presumption that Eurostar would continue to use North Pole depot, so with all things taken together it made sense to standardise on OHLE on the majority of the NLL.
I thought it was converted for Regional Eurostar?The remaining oddity is why 3rd rail continues into Euston despite all tracks being wired.
It must make life very complicated on that final mile with mixed electrical systems.
Not sure if you miss quoted, but I am certain that regional eurostar never planned to come into Euston!I thought it was converted for Regional Eurostar?
Presumably because of the preference for doing it whilst stopped, which would mean stopping on the slows next to carriage sidings which would affect timekeepingThe remaining oddity is why 3rd rail continues into Euston despite all tracks being wired.
It must make life very complicated on that final mile with mixed electrical systems.
What is the normal level of current ( i.e. amps ) in both these systems?In a dual electrified area, the safety concerns must take precedence, so comprehensive bonding is provided, giving massive opportunity for the DC current to stray and cause damage to structural metalwork and underground utilities. The AC return current is much less of a problem if it strays as there isn't the same corrosion problem with AC and the current is so much smaller due to the high supply voltage. Stray current immediately became a problem on the NLL which concentrated minds on removing as much of the 3rd rail as possible except for unavoidable short changeover sections. For the DC lines running into Euston from Camden I believe some mitigations have been applied such as parallel reinforcing conductors, and while the fairly limited service and small trains involved don't produce the high levels of DC return current in rails south of the river, there must still be some effect and long term it makes sense to decommission the 3rd rail and have the Watford trains switch to overhead for the final run into the terminus.
Exactly this ^ISTR there were some lengthy stretches of dual electrification when the OHLE was first installed for freight on the NLL. This is undesirable beyond necessary short sections for changeover as there's a conflict in the earthing standards between the two systems. In DC only areas, the rails are not earthed, to encourage the large return current to stay in the rails en route back to the substation instead of taking all kinds of alternative paths through the ground and any metallic objects in the vicinity, which are at risk of damage by a form of corrosion caused by the current. By contrast, in AC areas, the traction return rail is earthed and bonded to every metallic object nearby, including electrification stanchions, signal gantries and bridges for safety with the high voltage used and to avoid the risk of dangerously high 'touch potential' that staff and passengers might otherwise be exposed to.
In a dual electrified area, the safety concerns must take precedence, so comprehensive bonding is provided, giving massive opportunity for the DC current to stray and cause damage to structural metalwork and underground utilities. The AC return current is much less of a problem if it strays as there isn't the same corrosion problem with AC and the current is so much smaller due to the high supply voltage. Stray current immediately became a problem on the NLL which concentrated minds on removing as much of the 3rd rail as possible except for unavoidable short changeover sections. For the DC lines running into Euston from Camden I believe some mitigations have been applied such as parallel reinforcing conductors, and while the fairly limited service and small trains involved don't produce the high levels of DC return current in rails south of the river, there must still be some effect and long term it makes sense to decommission the 3rd rail and have the Watford trains switch to overhead for the final run into the terminus.
I can't find any info online about the installed power of the class 710 units but let's assume they're rated at about 2000kW. To deliver that power at 750VDC a current of 2666A is required. The same power on 25kVAC would draw around 80A.What is the normal level of current ( i.e. amps ) in both these systems?
If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.I can't find any info online about the installed power of the class 710 units but let's assume they're rated at about 2000kW. To deliver that power at 750VDC a current of 2666A is required. The same power on 25kVAC would draw around 80A.
That was my “round numbers” memory too. A lot of current. I^2 R losses large.If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.
I can't find any info online about the installed power of the class 710 units but let's assume they're rated at about 2000kW. To deliver that power at 750VDC a current of 2666A is required. The same power on 25kVAC would draw around 80A.
Thank you both.If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.

I think maximum draw is around 4000amps or just over for 3rd rail and around 200amps for 25kV overheads? Means 12 car CIGs etc would be limited when accelerating? Know if too many trains left a London Terminus at once the power sometimes tripped due to excessive current draw so 3rd rail quite limited. Know a 2 car EPB wasn't ever going to cause these sorts of problems on NLL!If I recall correctly, a typical four car unit such as a CIG, CEP or VEP drew about 2000A when pulling away.