The RAIB report does not state whether any train prior to 1B67 had reported the AWS Fault (Code 2) at WH154 signal, although there is mention of a subsequent report. Which presumably indicates that although the magnet was too low, its effectiveness was only impaired for a tiny fraction of the number of trains approaching the signal displaying green, which makes the accident an even more tragic event.
AWS code 2 faults (horn sounding when a bell expected) are by far the most common reported AWS fault. Back when I was an S&T fault team leader, across the area we covered, it was not unusual to have around two code 2 faults per week. Granted, some weeks we had none, but some weeks we had more.
AWS code 2 faults have numinous causes, but typicality fit into one of these categories:
- Fault found to be with the track mounted equipment, the cables or connections to this equipment or the control circuit from the lineside location cupboard, or relay room (or interlocking). Sometimes multiple trains will report the same signal/AWS installation.
.
- Fault found to be a problem with a particular train/unit/loco/cab. Often identified because the same train reports multiple signals/AWS installations as faulty but no other trains do. And no problems are found when the track mounted equipment is checked and tested.
But there are also reports where no problems are found with the track mounted or track side equipment (or not at first) and nothing to indicate that it's a on train fault.
Sometimes the operation of an AWS electro-magnet is marginal. It works okay for most trains, but occasionally, a train will experience a code 2 fault. Some of the possible causes include (but not limited to): the electro-magnet height being low, the voltage to the coils of the electro-magnet being low (faulty power unit usually), poor or intermittent connections in the circuit to the coils of the electro-magnet or in the control circuit, one of the coils of the electro-magnet being open circuit (when it’s being operated in the 12V configuration) or where it’s been incorrectly wired.
The problem is made worse by not every driver reporting code 2 faults when they occur. This is a problem that the railway does not appear to notice. One of my standard questions that I used to ask the signaller was “how many drivers have reported this AWS as faulty?” to which the answer was normally “only one”. And in some cases, it could be two to six hours since the original report.
I know this because in the past, an S&T technician has accidentality left an AWS electro-magnet control circuit disconnected (so EVERY train that had a green aspect would get a horn), but despite lots and lots of trains travelling over the installation, only one, or occasionally, a couple of drivers reported the code 2 fault… And this has happened more than once… One installation had missing wires for the control circuit for over ten years (although this was on a freight line with the relevant signal protecting the junction where it joined the main lines, so I presume the drivers just assumed a horn at this signal was normal for the rare times they actually got a green).
Changing the height of an AWS magnet is a fairly rare thing that is done. It’s not a trivial thing to do. Normally the height is set when the AWS is installed, or when removed and refitted in connection with either track renewal work or renewal or replacement of the AWS magnets. You have to undo some large fixings (screws or bolts) and either turn the mounting plates the other way up, renew/replace them, or in very rare cases, fit packing under the mounting plates.
So if the height was found to be out of specification by that much (4mm is a lot for an AWS), it’s very unlikely to have changed that much over a fairly short time period. It has likely been incorrect for some time.