So this is a new one for me. On the 14.29 out of Euston to Glasgow. Stopped almost immediately on climb out of Euston due to a loss of power. Lost lighting and air conditioning.

A few minutes later the train manager told us there was an overhead line problem and driver was on the control expecting it to be sorted in a few minutes. Then power was restored and we are on our way.

Seems like an odd one. What might have happened there I wonder?
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

Sleepy

Established Member
Joined
15 Feb 2009
Messages
1,832
Location
East Anglia
Can be the supply from National Grid cut out for some reason briefly. Or a tree branch touching overheads in windy conditions.
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
3,575
Location
Lancashire
Circuit breaker tripped and the Electric Control Room Controller needed to allow time for any emergency reports ( a few minutes ) before attempting to reclose the breaker
 

Mcr Warrior

Veteran Member
Joined
8 Jan 2009
Messages
17,229
Circuit breaker tripped and the Electric Control Room Controller needed to allow time for any emergency reports ( a few minutes ) before attempting to reclose the breaker
Is that what actually happened, or the most likely cause?
 

modernrail

Established Member
Joined
26 Jul 2015
Messages
1,443
Yes, OLE tripped. Reset without issue.
How often does that sort of thing happen? Is the cause usually some sort of unabated surge that sneaks though whatever the safeguards are?

Could it also trip things on the train?We noticed the power sockets went and the guard reset them.
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
3,575
Location
Lancashire
How often does that sort of thing happen? Is the cause usually some sort of unabated surge that sneaks though whatever the safeguards are?

Could it also trip things on the train?We noticed the power sockets went and the guard reset them.
Quick outages are mostly due to birds frying themselves tree branches of other detritus blowing in the wind onto the OLE or very occasionally train fault prior to the train 25kV Main circuit breaker. I’ve never known a complete loss of Grid Supply that only lasts for a few minutes as refeeding arrangements take some time to carry out
 

occone

Member
Joined
8 Apr 2023
Messages
221
Location
Manchester
What kind of battery backup for auxiliaries do electric trains have? And how long will things like toilets, lights, and heating work for without overhead power?
 

Bald Rick

Veteran Member
Joined
28 Sep 2010
Messages
35,792
How often does that sort of thing happen? Is the cause usually some sort of unabated surge that sneaks though whatever the safeguards are?

The OLE trips, somewhere on the network, several times a day. Three things are the main causes:

1) problem with the train
2) wind blowing something into contact with the OLE
3) nobody knows.

It’s not an ‘unabated surge’ but the monitoring systems detecting a short circuit somewhere.
 

Crossover

Established Member
Joined
4 Jun 2009
Messages
9,493
Location
Yorkshire
What kind of battery backup for auxiliaries do electric trains have? And how long will things like toilets, lights, and heating work for without overhead power?
HVAC (Heating, Ventilation, Air Conditioning) will almost certainly stop as soon as power is lost - I am fairly sure that even through neural sections when the breakers open, the HVAC ceases for a while (indicated by the drop of noise)

For lighting there would be a point where it would drop to emergency lighting levels but I don't know what runtime would be expected of the full lighting/toilets after power has dropped and the train is running on the aux batteries
 

Archvile

Member
Joined
12 Feb 2023
Messages
126
Location
UK
What kind of battery backup for auxiliaries do electric trains have? And how long will things like toilets, lights, and heating work for without overhead power?

Pendo's auxiliaries will run for ~ 30 mins - 2 hours depending on whether pantograph is up or down (if left up, will discharge back to the OLE and run down quicker), condition of batteries, outside temperature etc.
 

mike57

Established Member
Joined
13 Mar 2015
Messages
2,391
Location
East coast of Yorkshire
if left up, will discharge back to the OLE and run down quicker
I find this strange, as this means that the train is energising the OLE, and I would have thought that would be a big no no on safety grounds. Very much the same issue as if you have a backup generator and dont isolate the incoming supply.
 

trainmania100

Established Member
Joined
8 Nov 2015
Messages
3,033
Location
Newhaven
Few years ago similar problem on approach to Blackfriars in a 387. Driver stopped on a gap in the third rail and had to roll back
 

Falcon1200

Established Member
Joined
14 Jun 2021
Messages
6,554
Location
Neilston, East Renfrewshire
How often does that sort of thing happen? Is the cause usually some sort of unabated surge that sneaks though whatever the safeguards are?

As @Bald Rick says, all the time! The Electrical Control Room (ECR) will wait for the specified time, IIRC 2 minutes, and if no adverse reports have been received, will re-energise; But if the overheads trip out twice more the power will not be restored until they have been checked. If the overheads trip and fail to reset, they are down, or at least damaged or compromised somewhere. That is when the fun starts!
 

Archvile

Member
Joined
12 Feb 2023
Messages
126
Location
UK
I find this strange, as this means that the train is energising the OLE, and I would have thought that would be a big no no on safety grounds. Very much the same issue as if you have a backup generator and dont isolate the incoming supply.

I don't know the exact mechanism. The VCB would be open if no OLE supply, but the instruction is to lower the pan if no supply for the reason mentioned above.
 

Elecman

Established Member
Joined
31 Dec 2013
Messages
3,575
Location
Lancashire
Pendo's auxiliaries will run for ~ 30 mins - 2 hours depending on whether pantograph is up or down (if left up, will discharge back to the OLE and run down quicker), condition of batteries, outside temperature etc.
I’m pretty sure it won’t be energising the OLE as that would be a very serious safety issue. But the compressors may be having to run to keep the panto up
 

modernrail

Established Member
Joined
26 Jul 2015
Messages
1,443
The OLE trips, somewhere on the network, several times a day. Three things are the main causes:

1) problem with the train
2) wind blowing something into contact with the OLE
3) nobody knows.

It’s not an ‘unabated surge’ but the monitoring systems detecting a short circuit somewhere.
Interesting, thanks Bald Rick!
 

Archvile

Member
Joined
12 Feb 2023
Messages
126
Location
UK
I’m pretty sure it won’t be energising the OLE as that would be a very serious safety issue. But the compressors may be having to run to keep the panto up

That rings a bell, most likely the reason. Compressors running = dead battery.
 

Horizon22

Established Member
Associate Staff
Jobs & Careers
Joined
8 Sep 2019
Messages
10,996
Location
London
How often does that sort of thing happen? Is the cause usually some sort of unabated surge that sneaks though whatever the safeguards are?

Could it also trip things on the train?We noticed the power sockets went and the guard reset them.

Regularly. Maybe it happens on each ECRO (Electrical Control Room Operator) desk once a day at least. Often it is (presumed to be) an unfortunate pigeon smashing into the OLE.

Normally it’s a “trip and close” which means if nothing is noted within a couple of minutes, it’s reenergised. If it trips again there’s a wider issue.

== Doublepost prevention - post automatically merged: ==

What kind of battery backup for auxiliaries do electric trains have? And how long will things like toilets, lights, and heating work for without overhead power?

Almost all electric trains ‘load shed’ by which critical components are kept on the longest; note “critical” does not include passenger comfort.

HVAC fails within minutes and then systems switch to emergency lighting. Toilets tend to last a little longer but not much. Then eventually the PA/CIS fails and normally the last thing to go is the cab GSMR. The whole process ranges from 60-120 minutes depending on the overriding conditions.

If it’s prolonged, pantographs should be lowered.
 
Last edited:

Nym

Established Member
Joined
2 Mar 2007
Messages
9,784
Location
Somewhere, not in London
That rings a bell, most likely the reason. Compressors running = dead battery.
The compressors (Air Supply Units) run off of the Auxiliary Supply that isn’t battery backed.

I’m not sure where this “pan up, more battery discharge” thing is coming from, other than a significant simplification for the train operators.

If (all) lighting was lost on a 390, that would have been an AUX Trip not just OLE.
An OLE drop out sets off (consequentially as a loss of the Auxiliary Converter Modules, thence Battery Charger Proven) several timers and voltage relays that routinely disconnect loads as they’re not needed.

Loss of most lighting on the other hand, that could have been from a loss of OLE, with some really, really unhealthy batteries. But given the requirements for service I’d doubt that would be the case
 
Last edited:

800301

Member
Joined
29 Dec 2022
Messages
536
Location
Essex
It must come from somewhere to be able to put them up when they aren't already connected to power?

The pantograph uses the same Main Air Res supply as the rest of the train, a compressor doesn’t have to be running to have the pan up as the main air res will still have pressure, until that drops which depends how how well sealed the system is and any leaks, it can hold pressure for quite a while.

While I don’t know the inns and outs of a 390, a 387 has a separate auxiliary compressor that does run on battery supply to just put the pan up if the train does not have sufficient air supply, I’ve not yet been in a situation where the train has had to use that system
 

Archvile

Member
Joined
12 Feb 2023
Messages
126
Location
UK
The compressors (Air Supply Units) run off of the Auxiliary Supply that isn’t battery backed.

I’m not sure where this “pan up, more battery discharge” thing is coming from, other than a significant simplification for the train operators.

If (all) lighting was lost on a 390, that would have been an AUX Trip not just OLE.
An OLE drop out sets off (consequentially as a loss of the Auxiliary Converter Modules, thence Battery Charger Proven) several timers and voltage relays that routinely disconnect loads as they’re not needed.

Loss of most lighting on the other hand, that could have been from a loss of OLE, with some really, really unhealthy batteries. But given the requirements for service I’d doubt that would be the case

Can you explain the mechanism behind the raised/lowered pan generating such a large difference in the time auxiliaries will be available for?

Is it as simple as pan up = compressor(s) running then?

The discharge theory was what we were originally told in the classroom, but I'm aware that the propagation of myths is rife on the railway, like neutral sections being there to prevent outages in one area affecting another area (apparently untrue/not the primary reason).
 

Nym

Established Member
Joined
2 Mar 2007
Messages
9,784
Location
Somewhere, not in London
Can you explain the mechanism behind the raised/lowered pan generating such a large difference in the time auxiliaries will be available for?

Is it as simple as pan up = compressor(s) running then?

The discharge theory was what we were originally told in the classroom, but I'm aware that the propagation of myths is rife on the railway, like neutral sections being there to prevent outages in one area affecting another area (apparently untrue/not the primary reason).

No, because as I alluded to, the pantograph being up makes little difference. Unless there are other systems that also shut down that draw on the battery.
(And I’m not digging my schematics out on Xmas eve)
 

cool110

Member
Joined
12 Dec 2014
Messages
835
Location
Preston
like neutral sections being there to prevent outages in one area affecting another area (apparently untrue/not the primary reason).
They do do that, but only as a side effect of separating areas on different phases or feeder stations. The primary reason for them is that those gaps can't be bridged together. To get 25kV between phase and earth you need 43kV between phases, which would be very bad to short out. Going between the same phase from different feeders isn't as bad at the site, but causes problems for the ECOs and NESO as their switching gets bypassed by energy flowing in the wrong direction.
 