What happens to the power supply in the event of damage or a complete dewirement?
What happens to the power supply in the event of damage or a complete dewirement?
The controllers will normally try to restore it after a few seconds in case it is a transient problem such as a vapourising pigeon, but if it cuts out immediately after 2 (?) attempts they will leave it isolated until they find out what the problem is.
It's possible, but unlikely, that the wires are left hanging close to the ground but haven't actually touched anything so they are still live.
Happened not too long ago and a Virgin driver was injured having received an electric shock whilst inspecting for ole damage on foot and not seeing the hanging wire in the failing light.
He had stopped his train having seen damaged overhead power supply wires ahead of it. Following a call to the signaller, he left his train and came close to, or made contact with, an electrically live wire which had broken and was low hanging. The train driver suffered serious injuries.
This accident occurred because one of the overhead wires had broken, was hanging down and was electrically live. Two previous trains had come into contact with this hanging wire and consequently tripped the power supply circuit breakers. Each time the circuit breakers had been reset by the Electrical Control Operators in accordance with procedures to make the overhead wires electrically live again.
If the live OLE touches the ground, a train, or any earthed parts of the OLE it will shut down within a fraction of a second, at least on 25kV. The controllers will normally try to restore it after a few seconds in case it is a transient problem such as a vapourising pigeon, but if it cuts out immediately after 2 (?) attempts they will leave it isolated until they find out what the problem is.
It's possible, but unlikely, that the wires are left hanging close to the ground but haven't actually touched anything so they are still live.
Lower supply voltages have lower fault currents so it is possible the power might not shut down if there is not a low-resistance path to earth. This can result in fires.
However repeating the search (electric shock caused by defective OLE) with a start date of 1950 doesn't bring up any other reports, so I think we can conclude this is a rare occurrence. Railways Archive's accident report search is so much more useful than RAIB's!
I was taught. If the current trips then they immediately try to reinstate. If it trips again then they wait for a minute, then reinstate. If it trips again, its left alone and investigated further.
Not sure how accurate that is nowadays.
There was an incident at St Pancras Intl in 2009 when live 25kv ohle fell onto the platform.