Hi,

Does anyone in here know what the situation with the OverHead Line Equipment (OHLE/OLE) is, when work needs to be carried out in canopies at overhead-electrified stations?

For example, workers need to be up in the canopies when refurbishing/restoring/repainting them, or working on 240V electricals (e.g. lights, information screens, cameras, 240V cables) or the 100V speaker lines, etc.

I understand that a person has to be a bare minimum of about 2.75 (round up to 3) metres away from uninsulated 25,000V wires, to avoid the likely consequences of being any closer than that, but I would've thought that further than that bare minimum is good practice.

Can anyone in here tell me exactly what happens with the O(H)LE when such work up in the canopies needs to be carried out?
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

The Planner

Veteran Member
Joined
15 Apr 2008
Messages
19,705
Hi,

Does anyone in here know what the situation with the OverHead Line Equipment (OHLE/OLE) is, when work needs to be carried out in canopies at overhead-electrified stations?

For example, workers need to be up in the canopies when refurbishing/restoring/repainting them, or working on 240V electricals (e.g. lights, information screens, cameras, 240V cables) or the 100V speaker lines, etc.

I understand that a person has to be a bare minimum of about 2.75 (round up to 3) metres away from uninsulated 25,000V wires, to avoid the likely consequences of being any closer than that, but I would've thought that further than that bare minimum is good practice.

Can anyone in here tell me exactly what happens with the O(H)LE when such work up in the canopies needs to be carried out?
Isolations
 

Skeletor

Member
Joined
15 May 2024
Messages
22
Location
Glasgow
You require a c permit and should be briefed by the Nominated person.

You can refuse to go up without an isolation if you come in 2.75m of the infrastructure as you said.
 
Last edited:

Peter Mugridge

Veteran Member
Joined
8 Apr 2010
Messages
17,847
Location
Epsom
You can refuse to go up without an isolation if you come in 2.75m of the infrastructure as you said.

Most canopies I have seen carry a warning notice saying "no access without isolation" or similar; how likely is it that any work would be booked without an isolation also being booked in the first place?
 

edwin_m

Veteran Member
Joined
21 Apr 2013
Messages
28,692
Location
Nottingham
Never, ever without an isolation. All pre-planned work has to be risk assessed. If its not safe dont do it!
As does work that isn't pre-planned.

Even at a non-electrified station, a lot of canopy work is likely to require a line block due to the hazards of passing trains.
 