Electrifying Mainlines for Battery Train operation (using Class 897 as an example

Nottingham59

Established Member
Joined
10 Dec 2019
Messages
3,328
Location
Nottingham
This thread is to discuss the electrification needed on mainlines for 125-mph capable battery trains.

To start things off, these are my thoughts for main lines in my part of the world (i.e. the MML and the Cross Country route)

BEMU SPECIFICATION
It seems to me that the 10-car Class 897 trimode, or similar, as ordered by LNER would be a good candidate for modelling the OHLE needed for batterifcation of mainlines. The 897 has a claimed range of 120 miles on batteries, after which the diesel engines would need to be run. We don't have the full 897 specification, so I'm going to assume the following:
  • Maximum range on battery alone: 120 miles
  • Usual operating range (80% to 20% charge): 60% x 120 = 72 miles
  • Time to recharge (20% to 80%): 18 minutes (This is equivalent to a "2C" recharge rate)
  • Time to recharge (80% to 90%): 6 minutes (1C rate)
  • Time to recharge (90% to 100%): 12 minutes (0.5 C)
  • Maximum power draw: 6MW (with supplementary pantographs for use only when stationary or moving slowly)
INITIAL OVERHEAD ELECTRIFICATION
To start off, I'm assuming that we wire all sections of routes which carry 7 or more trains per hour in each direction. According to this thread, that means Nottingham-Trent East (7tph); Dore-Sheffield (8tph), Sheffield-Meadowhall (11tph). Also Bristol TM to Parkway (~7tph)

Other wiring could be added as needed, but these would not be a pre-requisite for running 897s with their diesel capability.

NOTTINGHAM-LONDON
With several hours under the wires, all Down trains will pass Wigston with 100% charge. 25 miles to Trent East will take that down to ~80%, followed by at least 18 minutes to recharge (6 transit; 6 dwell; 6 transit), taking them back up to 100% again by Trent East on the way back south.

SHEFFIELD-LONDON
Wigston-Dore is 65 miles, easily within the operating range of the 897. Dore-Sheffield is ~5 minutes each way and most London trains have at least 15 minutes dwell or more at Sheffield. State of charge: Wigston 100%, Dore 45%, aSHF 62%, dSHF 90%, Dore 97%, Wigston 42%. Easily done without diesel.

EDINBURGH-PLYMOUTH
Southbound Cross Country services will be 100% charged at Moorthorpe, and will still have 87% charge by Meadowhall, restored to ~97% in the 12 minutes from Meadowhall to Dore. 76 miles to Birmingham (36%). 6 mins dwell at New St (56%) plus 12 mins to Kings Norton (85%); 75 miles to Westerleigh Jn (22%). 20 minutes under the wires will get back over 80% leaving Temple Meads, which is enough to get to Tiverton before having to start the diesels. Then run on Diesel and Battery to Plymouth and back to Temple Meads.

CARDIFF-NOTTINGHAM
Trains will leave Severn Tunnel Junction with 100% charge. 73 miles to Bromsgrove (39%); 6 mins to Longbridge (59%); 2 miles to Kings Norton (57%); 12 min to New St (77%), plus 6 min dwell (82%); 50 miles to Trent East (40%). At least 18 mins to recharge at Nottingham (~90+) before passing Trent East heading back south

CONCLUSION
So it seems to me that with trimodes similar to Class 897 you can batterify the entire MML mainline and Cross Country route as far as Tiverton with just 10 route miles of OHLE at Meadowhall-Dore, 7 miles Trent-Nottingham and 5 miles between Briston Parkway and Temple Meads.

The key characteristic for the BEMU is a fast recharge rate under the wires. This dramatically shortens the length of wiring needed at each island of electrification.

Is this analysis realistic? What are your thoughts?
If you don't think it would work, what size battery would be needed?
 
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

Zomboid

Established Member
Joined
2 Apr 2025
Messages
2,226
Location
Oxford
Batteries depend on the chemistry used, the max/ min state of charge and charging rate, all of which will be balanced against the desired lifespan of the batteries. Ambient temperature impacts the ability to charge and discharge efficiently, and I've no idea what the 897 claims are based on.

There's a lot of assumptions in your analysis, and it's likely that initially at least a fairly conservative approach will be taken, and if similar chemistry to most cars is used they'll usually operate in the 20-80% state of charge range.

Also, the what bits to electrify debate will also depend on external factors, such as where a supply is available, and the required resilience of the supply. 897s having diesel means lower resilience would be acceptable for those, but that's not where things really should go in the medium term - getting rid of the diesel entirely should be the target.
 

hwl

Established Member
Joined
5 Feb 2012
Messages
8,240
This thread is to discuss the electrification needed on mainlines for 125-mph capable battery trains.

To start things off, these are my thoughts for main lines in my part of the world (i.e. the MML and the Cross Country route)

BEMU SPECIFICATION
It seems to me that the 10-car Class 897 trimode, or similar, as ordered by LNER would be a good candidate for modelling the OHLE needed for batterifcation of mainlines. The 897 has a claimed range of 120 miles on batteries, after which the diesel engines would need to be run. We don't have the full 897 specification, so I'm going to assume the following:
  • Maximum range on battery alone: 120 miles
  • Usual operating range (80% to 20% charge): 60% x 120 = 72 miles
  • Time to recharge (20% to 80%): 18 minutes (This is equivalent to a "2C" recharge rate)
  • Time to recharge (80% to 90%): 6 minutes (1C rate)
  • Time to recharge (90% to 100%): 12 minutes (0.5 C)
  • Maximum power draw: 6MW (with supplementary pantographs for use only when stationary or moving slowly)
INITIAL OVERHEAD ELECTRIFICATION
To start off, I'm assuming that we wire all sections of routes which carry 7 or more trains per hour in each direction. According to this thread, that means Nottingham-Trent East (7tph); Dore-Sheffield (8tph), Sheffield-Meadowhall (11tph). Also Bristol TM to Parkway (~7tph)

Other wiring could be added as needed, but these would not be a pre-requisite for running 897s with their diesel capability.

NOTTINGHAM-LONDON
With several hours under the wires, all Down trains will pass Wigston with 100% charge. 25 miles to Trent East will take that down to ~80%, followed by at least 18 minutes to recharge (6 transit; 6 dwell; 6 transit), taking them back up to 100% again by Trent East on the way back south.

SHEFFIELD-LONDON
Wigston-Dore is 65 miles, easily within the operating range of the 897. Dore-Sheffield is ~5 minutes each way and most London trains have at least 15 minutes dwell or more at Sheffield. State of charge: Wigston 100%, Dore 45%, aSHF 62%, dSHF 90%, Dore 97%, Wigston 42%. Easily done without diesel.

EDINBURGH-PLYMOUTH
Southbound Cross Country services will be 100% charged at Moorthorpe, and will still have 87% charge by Meadowhall, restored to ~97% in the 12 minutes from Meadowhall to Dore. 76 miles to Birmingham (36%). 6 mins dwell at New St (56%) plus 12 mins to Kings Norton (85%); 75 miles to Westerleigh Jn (22%). 20 minutes under the wires will get back over 80% leaving Temple Meads, which is enough to get to Tiverton before having to start the diesels. Then run on Diesel and Battery to Plymouth and back to Temple Meads.

CARDIFF-NOTTINGHAM
Trains will leave Severn Tunnel Junction with 100% charge. 73 miles to Bromsgrove (39%); 6 mins to Longbridge (59%); 2 miles to Kings Norton (57%); 12 min to New St (77%), plus 6 min dwell (82%); 50 miles to Trent East (40%). At least 18 mins to recharge at Nottingham (~90+) before passing Trent East heading back south

CONCLUSION
So it seems to me that with trimodes similar to Class 897 you can batterify the entire MML mainline and Cross Country route as far as Tiverton with just 10 route miles of OHLE at Meadowhall-Dore, 7 miles Trent-Nottingham and 5 miles between Bristol Parkway and Temple Meads.

The key characteristic for the BEMU is a fast recharge rate under the wires. This dramatically shortens the length of wiring needed at each island of electrification.

Is this analysis realistic? What are your thoughts?
If you don't think it would work, what size battery would be needed?
A couple of major misconceptions:
[0. You would give any CAF engineers reading that a heart attack!!! and engineers elsewhere would spill their popcorn or coffee]
1. No one (UK or globally) is proposing BEMU operation above 100mph on battery as the energy usage is too high. DfT, NR, RSSB, operators and OEMs are all aligned on this.
2. 897 operation on diesel or battery is targeted on secondary routes where the maximum lines speeds are in the 65-75mph bracket with 70mph max specified off OHLE. E.g. Doncaster - Hull (~70miles return trip off wires and will use some diesel in reality and not just battery on this route this should tell you something about battery range! or rather lack thereof), Leeds - Harrogate (~34miles return trip off wires, battery only) and Newark - Lincoln ~33miles return trip off wires (battery only); and potentially but unlikely according to "Plan A" Northallerton - Middlesborough (still 801s in the future) with ~42.5 return trip miles off wires. The real range will be much lower than you state and under much friendlier conditions.
3. In practice 897 mileage ranges are based on operating at those lower speeds with lower energy requirements, not mileage at higher speeds. The CAF 397 data says resistance (davis eqn on the level) at 70mph is just 39% of 125mph, but as always there would be greater hotel / aux. usage per mile at lower speeds.
4. 897s will have very tame gentle battery usage cycles with at least 4hours (slow) charging between battery usage off wires. (What you are proposing isn't kind to batteries)
5. Aux /hotel usage during long layovers in the off wires termini will also nee to be accounted for
6. The only source for the 120mile range is "The Anonymous Widower" asking google ai in April 2026 and then writing it in his blog. His conclusion was that most of the google info was from a Railway Gazette /Rail business UK article in early 2026, however there is no mention of 120mile range in the article when I checked, hence 120miles range may be just an AI hallucination.

As @Zomboid correctly states a huge amount depends on battery chemistry and duty cycles
7. Rail usage clocks up charge and discharge cycles quickly hence you need to be really kind to batteries to get any decent working life out of them - operating any current batteries technology at those C rates will lead to a very short life. The most expensive LTO cells which are best optimises for cell life cycle and high C rates are only good to 1.7C max other chemistry cells shouldn't be taken much above 1C (for 20% --> 80% and even lower elsewhere) if you want to maximise cell life. (As cross sector comparison the new Tesla taxi is targeted to spend ~ half its time every day charging at moderate rates to be kind to the batteries)
8. Much more mileage will be need to be electrified than some people want to believe. Siemens advertorial in Modern Railway late last year was pretty much on the money roughly stating: "you need the right ~30% electrified as a minimum" and that is for regional rather than IC use.

897s and the new batch of Hitachi 8xx for First Lumo/Hull aren't a good benchmark for intercity modelling as they all target lower speeds and shorter of wires distances - they are targeted at the easy low hanging fruit.

[As someone with very good knowledge of Bombardier/Alstom, CAF, Hitachi, Siemens and Stadler rolling stock]
 

GRALISTAIR

Established Member
Joined
11 Apr 2012
Messages
10,472
Location
Preston Lancs
1. No one (UK or globally) is proposing BEMU operation above 100mph on battery as the energy usage is too high. DfT, NR, RSSB, operators and OEMs are all aligned on this.
Power consumed is directly proportional to velocity cubed iirc? (Please trust me, I do know the difference between energy and power) - also related to resistance/friction/drag etc.
 

hwl

Established Member
Joined
5 Feb 2012
Messages
8,240
Power consumed is directly proportional to velocity cubed iirc? (Please trust me, I do know the difference between energy and power) - also related to resistance/friction/drag etc.
Yes. Force is proportional to v^2 (+ v + C + Potential Energy from elevation change) and Power is v^3 ([Force egn] *v), Energy is more complex on passenger trains as Hotel and aux loads /mile go up as you travel more slowly - the battery is best though of a bucket with a hole in it to represent hotel and aux loads, hence on battery there is an optimum compromise speed band to be ascertained between compromising for lower total power for hotel and aux if you go faster and lower total power due to dynamic resistances if you go slower (if you go too slowly traction system efficiency also drops which is another reason for not going to slowly!) Goldie Locks had lots of very relevant transferrable lessons on porridge to say on this!
 

brad465

Veteran Member
Joined
11 Aug 2010
Messages
11,398
Location
Taunton or Kent
On the XC network most of the 100+mph running is already electrified; Birmingham-Derby is the main exception, but this would be prime for electrifying anyway.
 

Nottingham59

Established Member
Joined
10 Dec 2019
Messages
3,328
Location
Nottingham
Power consumed is directly proportional to velocity cubed iirc? (Please trust me, I do know the difference between energy and power) - also related to resistance/friction/drag etc.
Yes, it is - at high speeds where air resistance is the principal load. (But since the train gets there faster, energy consumed per mile is proportional to square of the speed.)

The best benchmark I know for the power required for high speed running is the Euston-Glasgow record attempt back in 2021, where a 9-car Pendolino used less that 8MWh to travel 400 miles in just under 4 hours. So an average consumption of less than 2MW.


ENERGY
Net energy used for the journey was 7,863kWh after regenerative braking returned 13% to the supply. This gave an average consumption of 12.2kWh/km,
 

GRALISTAIR

Established Member
Joined
11 Apr 2012
Messages
10,472
Location
Preston Lancs
On the XC network most of the 100+mph running is already electrified; Birmingham-Derby is the main exception, but this would be prime for electrifying anyway.
You would think so -I am an electrification enthusiast. However, I will never on this forum use the dreaded phrase ---- en oh br ayn err !
 

hwl

Established Member
Joined
5 Feb 2012
Messages
8,240
On the XC network most of the 100+mph running is already electrified; Birmingham-Derby is the main exception, but this would be prime for electrifying anyway.
You would think so -I am an electrification enthusiast.
And some of the more problematic bridges at the Birmingham end are being dealt with by HS2.

== Doublepost prevention - post automatically merged: ==

Yes, it is - at high speeds where air resistance is the principal load. (But since the train gets there faster, energy consumed per mile is proportional to square of the speed.)
The problems is the force available for acceleration decreases with speed hence increasing timing taken to accelerate to higher speeds means the energy consumed is greater than squared / unit distance when you look at real routes with non-steady state assumptions. On most GB routes /services substantial proportions of the overall distance are spent accelerating /decelerating rather than cruising at speed. Simplification is not kind to battery modelling unfortunately.
 
Last edited:
Joined
5 Aug 2015
Messages
872
Location
Norfolk
Another consideration is existing power supply.
Southbound Cross Country services will be 100% charged at Moorthorpe,
Although the ECML recently underwent a PSU, it was unfinished north of Newcastle and is basically only capable to reasonable supply the last big December timetable change. The infrastructure on the ECML as it currently is would not be able to support XC trains even operating as 125mph EMUs let alone further draw for charging even if it's spread over the distance between Leeds and Edinburgh.
73 miles to Bromsgrove (39%); 6 mins to Longbridge (59%); 2 miles to Kings Norton (57%); 12 min to New St (77%), plus 6 min dwell (82%);
Similarly I highly doubt Winson Green and Galton Jnc feeders can handle any of that. Also depending on a dwell at New Street seems perhaps unwise when the timetable around there is so fragile, I know it's only a few percentage points but I wouldn't include it in a sketch like this. The power supply in the West Midlands in general is already a pinch point without any further electric traction than we have right now. Some intention exists from NR to address this put I haven't heard of even a plan yet.
With several hours under the wires, all Down trains will pass Wigston with 100% charge....
Trains will leave Severn Tunnel Junction with 100% charge.
It is indeed more likely that MML and GWML have electrical headroom available - but I still don't think it's at all certain that those lines can simply deliver the required power with no interventions. The majority of the MML is still classically fed although some passive provisions were made for retrofitting AT and all the feeder stations can provide that. It's also worth considering what the implications are of an N-2 situation at St Brides (Newport), or any of the 3 MML feeders (Braybrooke, Long Meadow Farm, Borehamwood)
with just 10 route miles of OHLE at Meadowhall-Dore, 7 miles Trent-Nottingham and 5 miles between Briston Parkway and Temple Meads.
But I raise this all because, no - you already need a lot more infrastructure investment then just that even for the favourable conditions this analysis relies on. PSU projects are really quite expensive although luckily somewhat straightforward.

2. 897 operation on diesel or battery is targeted on secondary routes where the maximum lines speeds are in the 65-75mph bracket with 70mph max specified off OHLE. E.g. Doncaster - Hull (~70miles return trip off wires and will use some diesel in reality and not just battery on this route this should tell you something about battery range! or rather lack thereof), Leeds - Harrogate (~34miles return trip off wires, battery only) and Newark - Lincoln ~33miles return trip off wires (battery only); and potentially but unlikely according to "Plan A" Northallerton - Middlesborough (still 801s in the future) with ~42.5 return trip miles off wires. The real range will be much lower than you state and under much friendlier conditions.
So perhaps on a good day, you could get from Doncaster to Hull and back off wires, but because realistically you can't depend on that, the whole fleet has to lug around all the diesel equipment as well even though the batteries are dependable for Harrogate and Lincoln routes. I mean, does it not seem a little absurd that we're building trains with diesel engines, fuel tanks, generators, traction batteries, a 25kV transformer and at least a pantograph all because we somehow can't do what the majority of continental railways did in 20th century. We know that bi-modes cost substantially more than EMUs upfront and will have higher maintenance costs too, tri-modes even more so. If you have to carry around a whole diesel engine, I can't personally understand how it's justifiable to also have the batteries - all just for platform air pollution? I guess the maintenance will be a bit cheaper if the engines are hardly used, but the track will nonetheless feel the brunt.
 

Crithylum

Member
Joined
21 May 2024
Messages
329
Location
London Borough of Ealing
Taking the pendolino example of 8MWh, with an energy density of 160 w/kg (roughly middle of the range for new LFP or sodium batteries), that would require 50 tonnes of batteries.

At a cost of £100/kwh (which is on the high end for these chemistries), that comes out to £800,000.

I’m not going to call either of these negligible, however, in the grand scheme of things it is only a few percent of the total cost. This is to cross most of country at 125mph.

Batteries of these chemistries can achieve roughly 5000-10000 cycles (maybe more for future sodium ion batteries), so assuming ~3 runs per day, that is approximately 5-10 years lifespan. I would be surprised if the lifecycle cost was even a fraction of the upfront and maintenance cost increase of a DMU.
 

Zomboid

Established Member
Joined
2 Apr 2025
Messages
2,226
Location
Oxford
The issue isn't really battery capacity, it's charging speed (I doubt you're getting 5000 cycles at maximum charge rate without seriously degrading the end of life capacity) and conservation of energy.

Batteries aren't magic, they're an energy store. If it takes 8MWh to get from Glasgow to London in 4 hours, then if it's fully electrified that's an average of 2MW. If it's 50% wired (by journey time) then that system has to deliver 4MW whilst the train is drawing current. If it's 25% then the draw is 8MW. Multiply that by a few trains and you're taking a lot of power in a short time, the grid connections and the OLE have to be designed to handle that.

And that's before we consider the losses associated with energy conversion into and out of storage. Assuming 90% round trip efficiency (which is quite ambitious as I understand it), that 8MWh is now 8.8MWh. If the grid sites are battery backed to ensure the load is manageable by the grid, we're potentially putting that energy in and out of a battery twice, so 8MWh consumed could now be up to 9.8MWh.

Personally I think batteries have a big part to play in the future of traction power, but they are not the silver bullet that will solve every problem, especially when it comes to higher speeds and long distance operation.
 

GRALISTAIR

Established Member
Joined
11 Apr 2012
Messages
10,472
Location
Preston Lancs
Another consideration is existing power supply.

Although the ECML recently underwent a PSU, it was unfinished north of Newcastle and is basically only capable to reasonable supply the last big December timetable change. The infrastructure on the ECML as it currently is would not be able to support XC trains even operating as 125mph EMUs let alone further draw for charging even if it's spread over the distance between Leeds and Edinburgh.
At an absolute minimum it would need Marshall Meadows to be SFC / AT to be installed and commissioned.
 